110V DC Floating Earth Ground Fault
BenM_Uk
Good morning all,
I have found this forum while searching for clues on a ground fault.
A 'ground fault' alarm came in over the weekend on the 110V charging system. We have two 110V fans currently running and I am suspecting that one is at fault but I can't turn it off yet to fault find. I say I suspect this as we have had to change them before because of low insulation resistance to earth. The motors are on a 3 wire DC system.
The measured voltage to earth on the running motors is
A - Earth 76V
AZ - Earth -44V
The output voltage is currently around 121-123V DC.
Now the strange thing for me is that when i turned on the 110V DC lights that run off the same batteries, the fault clears.
I then measured the voltage again at the motors and got the following
A - Earth -44V
AZ - Earth 76V
I am not 100% clued up on DC floating earth systems. If anyone can help educate me I'd appreciate it.
Ben
Sorted - I was drawn too much towards the motors due to past issues.
Ended up disconnecting one of the lighting circuits and all is well