Hello all,
If there is a specification requirement for a "100% HVAC redundancy requirement", what would you consider in terms of redundancy? Let me explain further.
For our particular situation for a small building that contains 2 rooms, each with AHUs capable of handling 100% of the load for that room, but they are all controlled from a central PLC. This PLC is not redundant, in the sense that if it fails, the system itself will fail.
The customer specified that "the HVAC system shall be 100% redundant".
From your position, how would you see this in terms of system design? We have interpreted it in the sense that the AHUs are designed such that if 1 of the 2 units fails in the room, the other unit can pick up the heating/cooling requirements. The customer interprets this as needing an additional PLC.
My argument is that where does redundancy stop if they go by that definition? Do we provide multiple AC/DC feeds to the units, multiple controller control cable paths, etc. I think the specification is poorly written and there are no grounds to enforce "100% redundancy" without a solid definition of exactly which components must be redundant.
Any ideas? This is coming from an electrical guy, so I would like to hear feedback from the community's experts in the field.
Thank you!
If there is a specification requirement for a "100% HVAC redundancy requirement", what would you consider in terms of redundancy? Let me explain further.
For our particular situation for a small building that contains 2 rooms, each with AHUs capable of handling 100% of the load for that room, but they are all controlled from a central PLC. This PLC is not redundant, in the sense that if it fails, the system itself will fail.
The customer specified that "the HVAC system shall be 100% redundant".
From your position, how would you see this in terms of system design? We have interpreted it in the sense that the AHUs are designed such that if 1 of the 2 units fails in the room, the other unit can pick up the heating/cooling requirements. The customer interprets this as needing an additional PLC.
My argument is that where does redundancy stop if they go by that definition? Do we provide multiple AC/DC feeds to the units, multiple controller control cable paths, etc. I think the specification is poorly written and there are no grounds to enforce "100% redundancy" without a solid definition of exactly which components must be redundant.
Any ideas? This is coming from an electrical guy, so I would like to hear feedback from the community's experts in the field.