we are starting up a 100 kW power plant meant to export 100% power to the grid. The plant consists of an internal combustion engine driving an asynchronous (induction) generator. The generator has a rated power factor of 0,85.
After a short test (50% rated power, about 10 minutes), the meter recorded ONLY reactive (capacitive) energy being exported, no real energy at all.
[ul]
[li]The grid operator installed a bi-directional meter (net meter)[/li]
[li]There are no power factor correction items in place[/li]
[li]The starting inductance is shunted 10 seconds after the main breaker closes (so the generator was directly connected to the grid during the test)[/li]
[/ul]
100% reactive power being exported really puzzles and worries me...
Meter readings follow:
Power import prior connecting the generator to the grid: 1.7 kW
Power import after connecting the generator to the grid: 0.0 kW [amp reading at generator was 77A]
Active energy exported: 0 kWh
Reactive (capacitive) energy exported R+C: 6 kVARh
Reactive (inductive) energy exported R-L: 0 kVARh
Not having any power factor correction I was expecting high reactive energy readings, but not 100%! Anyone knows what's going on here?
Thanks and regards.
we are starting up a 100 kW power plant meant to export 100% power to the grid. The plant consists of an internal combustion engine driving an asynchronous (induction) generator. The generator has a rated power factor of 0,85.
After a short test (50% rated power, about 10 minutes), the meter recorded ONLY reactive (capacitive) energy being exported, no real energy at all.
[ul]
[li]The grid operator installed a bi-directional meter (net meter)[/li]
[li]There are no power factor correction items in place[/li]
[li]The starting inductance is shunted 10 seconds after the main breaker closes (so the generator was directly connected to the grid during the test)[/li]
[/ul]
100% reactive power being exported really puzzles and worries me...
Meter readings follow:
Power import prior connecting the generator to the grid: 1.7 kW
Power import after connecting the generator to the grid: 0.0 kW [amp reading at generator was 77A]
Active energy exported: 0 kWh
Reactive (capacitive) energy exported R+C: 6 kVARh
Reactive (inductive) energy exported R-L: 0 kVARh
Not having any power factor correction I was expecting high reactive energy readings, but not 100%! Anyone knows what's going on here?
Thanks and regards.