Utilities are not my forte. Working in a city that either does a 1" tap or 2". Believe 2" is significantly more than we need, but not sure the 1" is sufficient. Providing water to a park pavilion, about 450' from the main and 20' higher in elevation. The pavilion has 2 urinals, 6 toilets, and two water fountains.
First time doing this, but I calculated this to be equivalent to 28 WSFU's. Believe a 1" good for about 20.
For the fire hydrant where we are tapping, fire department provided static pressure of 75, residual of 50 and then stated flow of 38. Realize need to get flows.
Wondering if the City does a 1" tap and we size up to 1 1/2" for the 450' run or so, if that would be beneficial or not?
Am I on the right track? Any help would be appreciated.