May 5, 2015 #1 thekman Electrical Joined Sep 3, 2009 Messages 90 Location US I have the 2008 NEC and cannot find the required wire size for a 1/2HP 24VDC motor, FLA=20A. I've been pinballing around as it tells me to...in a hurry as always...the tables it sends me to are all for ac voltages..
I have the 2008 NEC and cannot find the required wire size for a 1/2HP 24VDC motor, FLA=20A. I've been pinballing around as it tells me to...in a hurry as always...the tables it sends me to are all for ac voltages..
May 5, 2015 Thread starter #2 thekman Electrical Joined Sep 3, 2009 Messages 90 Location US 430.22 sends me to 430.6(A)(1), which sends me to tables 430.247-250, which are all ac motors...?? Upvote 0 Downvote
May 5, 2015 1 #3 flexoprinting Electrical Joined Sep 22, 2007 Messages 239 Location US Did you see the Exception note under (A)general in 430.22 if not read that, otherwise Amps AC or DC same thing. Chuck Upvote 0 Downvote
Did you see the Exception note under (A)general in 430.22 if not read that, otherwise Amps AC or DC same thing. Chuck