This is a cable sizing question. This really has to do for a design that must meet CEC, but I wouldn't mind feedback from the NEC folks as well, I do like to understand their methods too...
I have a bunch of continuous motor feeds that will go in a cable tray. These are for motors sized from 1HP up to 75HP. However, I do not know how many cables will be placed in this cable tray. I'm assuming it will be random filled and I'll derate the cables using the adjustment factors for more than 41 current carrying conductors . In the NEC this would be an adjustment of 35% (Table 310.15(B)(2)(a)), in the CEC this would be 50% (Table 5C).
If I had a continuous 50HP motor at 575V with a FLA at 50A. Will I pick the cable based as follows:
50Ax1.25x(adjustment factor) OR can I omit the 1.25% at this point because I'm sizing the cable larger than the 1.25 factor?
I would say no because the 1.25 factor is not really a de-rating but compensation for an overload motor condition and must be considered when adjusting the ampacity for the random filled cable-tray.
However, I'm not sure the logic/reasoning behind sizing conductors for transformers. Say I have a lighting transformer located somewhere in the field and again I have to feed it with a cable via the same cable-tray routing. Would I size the primary conductor as follows:
FLA*1.25*(adjustment factor), or can I omit the 1.25x?
In this case, I'm not really sure. The 1.25x was due to the fact that the primary breaker had to be derated for 80% for continuous use, so I'm in doubt if you need to keep the 1.25%.
Much appreciated,
Majesus
I have a bunch of continuous motor feeds that will go in a cable tray. These are for motors sized from 1HP up to 75HP. However, I do not know how many cables will be placed in this cable tray. I'm assuming it will be random filled and I'll derate the cables using the adjustment factors for more than 41 current carrying conductors . In the NEC this would be an adjustment of 35% (Table 310.15(B)(2)(a)), in the CEC this would be 50% (Table 5C).
If I had a continuous 50HP motor at 575V with a FLA at 50A. Will I pick the cable based as follows:
50Ax1.25x(adjustment factor) OR can I omit the 1.25% at this point because I'm sizing the cable larger than the 1.25 factor?
I would say no because the 1.25 factor is not really a de-rating but compensation for an overload motor condition and must be considered when adjusting the ampacity for the random filled cable-tray.
However, I'm not sure the logic/reasoning behind sizing conductors for transformers. Say I have a lighting transformer located somewhere in the field and again I have to feed it with a cable via the same cable-tray routing. Would I size the primary conductor as follows:
FLA*1.25*(adjustment factor), or can I omit the 1.25x?
In this case, I'm not really sure. The 1.25x was due to the fact that the primary breaker had to be derated for 80% for continuous use, so I'm in doubt if you need to keep the 1.25%.
Much appreciated,
Majesus