cdi12
Structural
- Jul 1, 2006
- 38
I have designed canopy spread footing using load combination 0.6D+W and 1.0 factor of safety for overturning and uplift but reviewer wants me to use FOS=1.5 It looks very conservative to me and I could not find this in IBC. However PIP STC01015 Structural Design Criteria Section 4.3.7.2 is very specific:
The minimum overturning "stability ratio" for service loads other than earthquake shall be 1.5 For foundation design of building and open frame structure, if the dead load factor is 0.6 in accordance with SEI/ASCE 7, Section 2, the minimum overturning "stability ratio" shall be 1.0
Also thread176-67397 dealt with similar question but no precise answer yet. Please share your thoughts/experiences. Thanks, IV
The minimum overturning "stability ratio" for service loads other than earthquake shall be 1.5 For foundation design of building and open frame structure, if the dead load factor is 0.6 in accordance with SEI/ASCE 7, Section 2, the minimum overturning "stability ratio" shall be 1.0
Also thread176-67397 dealt with similar question but no precise answer yet. Please share your thoughts/experiences. Thanks, IV