Phase-earth fault in YNd11 step-up transformer while operating at no load
BAHADIR AKBAL
Hello everyone
There is a YNd11 step-up transformer in a factory. When the star point of the transformer is grounded, the protection relay gives a phase ground fault approximately 20 minutes later. The same problem occurs when the delta winding of the transformer is completely unloaded. The star side is at 33 kV, the delta side is at 6.3 kV. If the star point is not grounded, it does not give a fault. The fault current is reported by the protection relay as approximately 30 A. It is a great risk for the star side to work without grounding. However, when grounding is done, the protection relay trips. Do you have any information on this subject? Can the 3rd harmonics in the network or in the transformer's idle operation reach the level of 30 A?
Unbalanced primary phase voltages or pri9mary phase angles.
In these cases, I think the protection relay opens immediately. However, approximately 20 minutes after the power is applied, the protection relay opens the breaker. 20 minutes is a very long time in such cases. Could there be another reason?For example, a partial discharge in a cable. Can this last for 20 minutes?
An overcurrent element just above pickup can take an excruciatingly long time to trip.
What type of relay? If it's a digital relay, you should be able to review the fault data including the current phasor data. Make sure the CT polarities are correct. If the relay is summing the phase current numerically, it can nuisance trip if one of the phase ct's is wired incorrectly.
Any unbalance in the incoming power and the delta will cause a neutral current.
This may be misinterpreted as a ground fault be the protection.
Could you please share with the members,
1) SLD of the protective relay scheme of the transformer?
2) Which relay has operated?
3) Its settings?
To confirm, does the main power feed the wye side of the transformer? Is the main power feed derived from a grounded Y transformer?
I ask because it’s more typical in my experience for the source to be grounded, and the loads, such as this transformer, run ungrounded. This prevents the load (specifically the bank itself is a ground fault path) from feeding back to faults on the primary and de-sensitizing the overcurrent protection on the source.
Can you confirm the power is provided via the Y size? Why then would it be a problem to lift the neutral connection?
The neutral connection is probably providing ground current detection.
What are the primary voltages?
Line to line and line to neutral?
It is possible to have equal line to neutral voltages along with unequal line to line to line voltages. This is quite common in long rural lines with mostly line to neutral loads.
Either condition will cause a circulating current in the delta, which in turn will cause a current to ground in the primary.
