Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Energy gases (COG, BGF and BOFG) are mixed, and the result is called BLG (“blandgas”). This gas will be fed a CHPP.Is that a gas pipeline feeding the blast furnace? Or exhaust gases from the blast furnace? Would the area be explosive (i.e. classified)?
I believe the pipe with energy gases (COG, BGF and BOFG) could be classified and we are aware to leave a minimum distance to it. Apart of ATEX could be another issue related with EMC. Yes the pipe has high temperatures (I do not know the value).Are the cables passing through a hazardous area as classified by the applicable code?
The cables may or may not need to be rated for hazardous locations.
Are the cables passing through an area of high ambient temperatures?
The cables may need to be de-rated, or a higher temperature rated cable may be needed.
At lower voltages, Mineral Insulated cables may meet both hazardous location requirements and high ambient temperature requirements, with suitable de-rating.
Thanks however I mentioned pipe gas and not come conveyor.Usually, the coke used in a Blast Furnace is conveyed as solid particles of 100-200 grams from the storage to the highest level of the blast furnace and introduced from here together with the ore and other materials through open conveyors.
If the cables are insulated, shielded, and grounded, no distance is required from the power cable tray to the coke conveyor. Maybe if the coke catches fire, the intersection place has to be protected by fire protection.
See NFPA 850 paragraph 7.4.4 coal conveyors, for instance.
In my opinion, paragraph 7.4.5 it is also interesting [Coal Conveying and Handling Structures].
