Shear strength of fastener in plywood
Does anyone know of a good reference to calculate the shear strength of a single fastener in shear in plywood? I tried looking at NDS, but nothing really comes to mind. Trying to connect a light gauge strap to sheathing. The tables for the sheathing in NDS don't really apply because the way the load is applied, the plywood sheathing transfers load to to the strap, not a piece of framing below. To simplify the question here, Imagine I'm trying to analyze simply the strength of a single bolt/nail/screw in plywood
Probably not exactly what you are looking for but see table below. I've used these values before when designing plywood gussets that are attached to 2x framing....
I wholeheartedly disagree. The stud is a crucial part of that load path, unless you have sheathing with no horizontal joints. Possible in a single story building, not in anything larger. If this is between floors, you either take the uplift from the stud into the strap and into the stud below, or the same but using sheathing (SDPWS have some example details for using sheathing this way.)
If I'm misunderstanding your condition, please post a sketch.
Why wouldn’t the usual lateral dowel capacities apply? There’s 4 limit states, two of which are further split between main member and side member (for a total of 6). You could consider the plywood to be the main member and the strap to be the side member. There is also supplementary info on dealing with non-wood side members.
Why don't you just calculate the governing lateral capacity from the equations in section 12.3 of the NDS?
You have the properties of the wood (such as as the G value and thickness) and that of your fastener (yield strength, diameter). So set up an excel sheet, and plug and chug. Verify your sheet with values for variables in the NDS.
Also see Appendix I which discuss the failure modes that will be applicable to you (i.e., single shear vs double shear).
In the end, that is what I did. I would like to follow up to whoever sees this and point out that you also have to calculate the governing loads of the light gauge steel (tension, shear, screw bearing, pullover, etcetera...)
In case you missed it, E830 that @Ron247 shared above has what you are looking for.
