Easy foundation work or a trap? 2
ANE91
377
Local contractor sells underpinning services to homeowners. Jurisdiction requires a sealed engineering report before issuing a permit for the work. Their last guy retired; I’ve seen his work. Enter me: seems like a good potential source of revenue, low hanging fruit. Totally new line of work for me (though I’ve done basement wall repairs). Salient assumptions below:
1. No geotech report, but I could default to the lowest presumptive soil bearing pressures in IBC 1610 and 1806.
2. Contractor specializes in helical piers side-mounted to footings.
3. Contractor is likely promising to “fix the foundation” when they really mean that they’re arresting or at least attenuating settlement. No jacking applicable.
4. Loads are not high enough and walls aren’t long enough to warrant special attention for any eccentricity.
5. I cannot think of any codified reason for the jurisdiction’s requirement beyond the basic alterations stuff in the IEBC.
6. By and large, these aren’t life safety issues but rather serviceability concerns. I would pull in a geotech for a house that looks like it’ll disappear into a sinkhole or some such.
7. My reports would simply verify whether the contractor’s proposed underpinning sufficiently increases the bearing surface so as to justify an expected decrease in settlement, even though the house is probably done settling by the time they get involved…
The last point doesn’t 100% sit right with me. On the one hand, who am I to tell a contractor what he can/cannot sell? On the other hand, I doubt that I would find much of that work truly necessary. Would getting involved make me party to deceit?
As much as I like to make money, I hate trouble more. Can I get a sanity check on this, particularly from others who design underpinning? Feel free to tear me a new one; I can take it. Thanks.
For better or worse, I do a fair amount of these. The AHJ requires an engineer design and "sign off" post construction.
It is basically showing helical piers every 5-6 ft with the footing notched out for the bracket. For sign-off, we use photos and the boring log showing install pressures that can be equated to capacity. Pretty much standard practice in my area so I am not being too much of a cowboy.
The foundation company provide a lifetime warranty so the risk is a bit mitigated. Have not had an issue in 20 years.
@ANE91 not sure about this comment specifically that you've made:
"On the one hand, who am I to tell a contractor what he can/cannot sell? On the other hand, I doubt that I would find much of that work truly necessary. Would getting involved make me party to deceit?"
No one is telling the contractor that they can't sell helical piles, or sell their services using said piles to relevel/stabilise foundations
However, assuming you were working in my country at least, the law dictates that they can't just cowboy their way through it
They are doing work to a house and there are performance standards set by the Building Code that they must comply with
Some of these relate to workmanship (their domain) but others require designer input
Does your contractor know the bearing demands? foundation strength? soil profile? - that's where you or someone else comes in
So it's not telling them "what they can sell": it's working with them to use their product to deliver compliant building work
I think one key thing that a few people mentioned here is jacking vs securing. Jacking a foundation is a totally separate service/ approach IMO. That is very rare around here and needs careful consideration. Geotech is a must and a thorough analysis. I usually only see those done w/ push piers, never helicals.
And I think there's a big difference between doing actual engineering on the repairs vs a report/ rubber stamping what a contractor puts together.
I never consider the the latter, but see a lot of work that those other companies/ engineers do. If we do site visits on 95% of the projects, those guys rubber stamping a title page for the contractor might do 10% or less. They are so disconnected from the projects that when something goes wrong (and it does quite a bit) they have no clue what the problem even was in the first place.
@jerseyshore yes I agree there are some differences but you still need to be careful even if you're just "securing".
Your assumption has to be that the foundation is point supported at the pile locations as the existing soil has shown itself to be inadequate to provide support (why else are you doing this?). You then need to check the as-built foundation for its ability to handle its Ultimate design loads (1.2G + 1.5Q, G + Eu, G + Wu, whatever) assuming that it is pointed supported.
Critically, there is always an eccentricity with this. I've used helical piles before, there's no practical way to get them central under the foundation. So not only do you have your Ultimate loads going onto the existing foundation as a spanning member instead of being fully supported, now you're sticking a wopping great torsional moment into the foundation. And, having extensively looked at this myself on some existing foundations, there is no real system to resolve that torsion without putting in new foundation beams.
Helical piles w/ underpinning brackets onto notched footings get the load as close as possible to concentric for retrofit conditions. When we have heavier loads or special conditions we'll try to alternate pile installation on both sides of the wall.
I will say that these helical piles, especially for repair/ retrofit conditions have mostly been installed around NJ since hurricane Sandy in 2012. I've seen very few issues with them besides the occasional contractor who cheaps out and only drills them 7 ft deep or something. Will be interesting to see how they hold up over the years.
Absurdly common in Texas. Ask me how I know...
If you are working in Texas, from what I have heard, you have an endless supply of potential work. Swelling soils are one of the main sources of helical anchor usage typically.
I would stay away from side-mounted. I worked a legal case where they did not chip back the concrete. The put the shelf of the anchor under the foundation, but it was on the outside edge, about 1' from the crawl space block wall. All they wound up doing was leveraging the foundation over and almost buckled the crawl space block wall. I excavated the entire rear of the house to show the anchor locations. This also exposed one of the cons the contractor used. Charged for 15 anchors, installed 12. But worse than that, they were charging for extra 7' shaft length beyond the 14' estimated. All of them took from 3-5 extra shafts, including the 3 they never installed. They had a sketch showing each location and the extra shafts.
I have never designed an underpinning project where I gave any kind of guarantee ESPECIALLY on expansive soils. I explain to the client up front that in essence, the house was built on soils that were not suitable for construction. There are original designs and repairs that can minimize the issues related to poor soils but cannot eliminate them nor get them to a universally accepted level of performance. If they do not like me putting a disclaimer on my design, I walk away from the job, but they know up front.
Sounds like you guys are tackling some of the issues there. Installing both sides of the footing would require cutting out the floor though - starts becoming a pretty hefty exercise in that case?
Preferred underpinning here is to excavate from the outside and pour discrete pads to stabilise or use as a base for jacking the foundation back to level
This has its share of limitations too though
Though I've done a few relevelling jobs with screw piles and not had an issue
Really depends. Most structures have a basement or crawlspace so going on both sides is not impossible for exterior walls. For interior or unit demising walls we like to alternate if possible.
The contractor that I mentioned above that we do 95% of this repair work with will never jack a foundation with helical piles. In fact I don't know anyone who would. Jacking foundations are incredibly rare with any type of system (by reputable contractors). Majority of the time it will be a stabilization of the foundation and if the client/ contractor want to get some re-leveling work then they jack the wood framing and shim between.
Interesting. It's relatively common here. I've seen it done with both permanent screw piles and temporary ones (lift the foundation off screw piles, grout underneath, disconnect piles)
So many houses are out of level here thanks to the earthquakes that there are a lot of relevelling contractors around
Admittedly, most of them are cowboys, but there are lots of ways to do the job properly too
Always interesting to hear how things are done in different places. Similar to how many people have concerns with expansive soils, but that's low on the list around here.
We have expansive soils elsewhere in the country but not in my city
Here, it's peat (the settlers decided to drain a huge swamp and build a city on it) and liquefiable soils that are the headache
We have a lot of peat, lot of muck, and a lot of nice jersey shore beach sand (which my house is on :) ).
The cowboy classic here is to use discrete underpinning pads to side jack an unreinforced rubble foundation (read: contains bricks, stones, and not much cement) on sites with shallow water tables and liquefiable materials at the water table
If the side lift doesn't break the foundation, the slow creep probably will as the unreinforced shitty foundation tries to span... and if not, the liquefaction punching in a future earthquake will finish it off :)
We do some minor jacking but rarely get carried away with it. Any jacking does require either pinning on both sides or one pin, but it is directly under the load to lift.
We also have to deal with the footings being able to span between jacks. Typically, only 5' to 6' spacing is used because of the footings. Had one client who spent $38k one time on someone who bragged about their jacks being stronger so they could space them 12'. Three years later he called me to come out and tell him what was wrong. The footings broke in between every pair of jacks during a dry spell. The company that did not get the job was $52k but was spacing them 6'. While saving $14k, he threw away $38k. Twice the jacks for 37% more money.
This is a crazy effective sales technique and I hear it far more often than I ever thought I would. I get that the average homeowner has no clue about structure, but this type of statement wins people a lot of jobs it seems.
I don't understand this. The contractor said they could do the job and they failed to do so. That would be illegal/non compliant work here and the contractor would be on the hook to fix it. Why was the client the one out of pocket?
There are a LOT of nuances with this work, and it doesn't sound like you're familiar with them all
Thanks for the photo. I’ve seen similar issues. You’re right that I’m not familiar, so I appreciate your insights. Gotta learn somehow, and better here to start than with an occupied building.
@XR250 is basically describing what my prospective client’s previous engineer did. Definitely no jacking for me. We also have rubble stone walls, which I’m not interested in messing with, either. Good points about eccentricity, notching, and staggering — it all comports with what I’ve read in Perko’s book.
I’ve carefully read everyone’s responses; thank you all. The fact is that there are engineers engaged in this type of work, and not always unethically. The consensus seems to be that site visits and borings are required. I’m struggling to reconcile that with how neither is ever done in residential. I mean, I carry around my own hand auger, and oftentimes I’ll send samples for Atterburg tests (~$200) or I’ll check USGS for soil data, but I’ve never seen anyone willing to pay for SPT on a house. I asked around at a recent ASCE event, and others just use the presumptive soil provisions in the IBC.
Need to stew on this some more. It’s possible I’m being too academic about the whole thing.
As I recall, contractor was no longer in business coupled with a discreet and somewhat hidden note about Owner being responsible for engineering design that never occurred. In essence, the note was "this is our idea of a repair, but it is the Owner's responsibility if it does not work"
