Help Calculating Ledger Connection
stilllearningPE
4
I am trying to add a 12'x36' raised deck to attached to my home with a ledger on one side and 4 posts on the other about 10 feet high. I can stamp the plans myself because I am licensed PE in Ca but am hesitant to do so because I don't fully understand the ledger to rim joist connection. The vertical loads I am concerned with are DL, LL, and uplift from W. I am assuming it is fixed joint connection and so will develop a moment. Dividing the moment by the lag screws spacing will give me the tension loads that need to be resisted in withdrawal. How would I calculate the moment since part of the deck is support by posts? Am I correct in my thinking or would this be a pined joint, and if so how would I calculate the withdrawal on the lag screws without a moment. I am having trouble conceptually and would appreciate any help to make sense of it. Thx
Sounds like this is typical wood deck construction, in which case I think your ledger connection is just a pinned support. You would just need to calculate the shear capacity of the fasteners.
Not sure about residential code in California, but in my area this is a prescriptive detail from the code that doesn't even require engineering...
I would normally treat that detail as pinned so you'd have a simply supported beam between the post and the ledger
However, the devil is in the detail with this
You are presumably putting this ledger up against your cladding and bolting through which:
1) potentially compromises your waterproofing/cladding
2) puts an eccentricity in the bolt as the ledger will be offset from the rim joist - this can cause rotation and cladding crushing. I've been involved with a settlement on a house (not my design thankfully) that had this exact issue (see photo)
The good news is that, as Trak said, there are usually standard details for this in your local building code - but make sure that it applies to your cladding system
To evaluate the lag bolt attaching the ledger to the existing structure, look at NDS's Technical Report No. 12 which gives modified equations for a gap between the two structural elements. Also ensure the lags occur at the existing studs, presumably @ 16", but should be field located prior to installation.
There is no standard detail for use in California that I am aware of.
  • AWC-TR12-1510.pdf
Thanks for the comments. I also thought this was a prescriptive but the plan check comments require a PE stamp. The plan check comment that is giving me pause and for which I'm hesitant to use my stamp is below which references withdrawal capacity. I can do a shear check on the lag screws due to vertical loads which is easy enough. I can also calculate the withdrawal capacity of lag screws using the NDS, but I'm not sure what to compare this against since a pinned joint doesn't develop a moment for me to convert to a pullout force by dividing by a distance (presumably vertical distance between the staggered lag screws on ledger which would form T/C couple causing some sort of prying action?) Sorry if this all sounds redundant. I haven't used my stamp before and I don't design work for a living. Any guidance would be much appreciated.
"Reference a detail at junction of exterior decking, wall and interior floor framing. Show elevations, flashing, anchorage and deck ledger requirements. Show a method of positive attachment of ledger to the structure that will resist vertical and lateral loads. Means of attachment must also resist withdrawal and must resist uplift for the entire total live load. Reference CRC Sec. R507.1 and Figure 507.2.3"
Thanks so much for the attachment!
It’s pinned. Refer to AWC’s deck guide.
Honestly, you may want to have another PE or even a contractor review your plans. Wood does not seem to be your forte.
Yes, I was thinking of doing something similar just to be safe. Are there any good books with structural design problems and practical solutions anyone could recommend to further my knowledge, or would that be the topic of another thread?
I read the plan check comments more as pointing to needed seismic anchorage back into the structure, rather than checking for withdrawal of the fasteners into the ledger. Did you provide connections for the deck back into the main structure, or did you design them as separate structures, and then check the effects for seismic pounding and drift of the deck?
