  1. WWTEng

    Baseplate to nut contact

    Picture is attached, although you can't tell that the foundation has tilted.https://files.engineering.com/getfile.aspx?folder=eea8bfd4-b4f9-4c22-825e-44284ad2ff59&file=20240801_125929.jpg
  2. WWTEng

    Baseplate to nut contact

    Hello, I have a situation where a steel column (exterior, W12) is leaning due to the foundation heaving about 3/4". The foundation is at least 30 years old, so is the steel. I guess the issue was recently notice by the facilities. In order to correct the issue "temporarily", the site crew...
  3. WWTEng

    12" CMU fire rating

    BA, I think you are correct. That appears to be a reference to horz reinforcement.
  4. WWTEng

    12" CMU fire rating

    Thank you all. @BA, just checked the drawings again. Built in 1972, in Chicago. The drawings show "Wall reinforcing every second block course". Which likely means grout @ 16" oc.
  5. WWTEng

    12" CMU fire rating

    I am looking at a 12" cmu wall from 1970s. The drawings appear to show the wall grouted @ 48" oc. I am trying for find some fire rating dates for CMU from that era but not finding anything. What be a good resource for this information? Thank you.
  6. WWTEng

    F1554-Gr 55 Gavlanized-Welded Studs

    Is there a load chart available for using these F1554 anchors as welded studs to a plate? Thank you.
  7. WWTEng

    CMU-Cantilever height

    I am looking at aprox 13' tall exterior CMU wall. Non-load bearing. Of course it will have to resists lateral loads (likely wind, since its Michigan). Before I start designing in detail, are there any cmu max height requirements for a cantilever wall? Thanks,
  8. WWTEng

    15' tall, 8" cmu wall, cure time?

    Single story masonry building with precast roof. Wall height aprox 15', 8" cmu. My question is about putting the roof (precast planks) on the wall once the wall is complete. How long should the contractor wait before placing the loading the wall with planks. Thanks.
  9. WWTEng

    Digging around 12' pier

    Consider a 3'x12' deep pier foundation supporting an out door structural column. The contact tor was supposed to pour a pipe within the concrete. The contractor forgot to do that. They are recommending digging down to one side of the pile 9' deep to install the pipe and fill the void with grout...
  10. WWTEng

    Smart grid

    What exactly is a Smart Grid?
  11. WWTEng

    Exp joint-190'x232'

    JAE. Thanks. My structure is concrete so I think I should be able to go 232' w/o a joint.
  12. WWTEng

    Exp joint-190'x232'

    190'x232' sports arena (single story). Roof is metal deck on steel trusses. The structure itself is concrete a frame (columns wand beams). The temp range is 90 F. But the project is an area where air-conditioning (heat and cooling) may not be functional. I can't decide if an building expansion...
  13. WWTEng

    Short circuit force direction

    Is Asymmetrical SC ever used in design? My understanding is that bus work as well as ground grid is designed for Symmetrical only.
  14. WWTEng

    Short circuit force direction

    Thanks Bill. Is SC force always horizontal (and perpendicular) to the bus? And typically of the three phases, does it develop only in two?
  15. WWTEng

    Short circuit force direction

    Consider a 138kv system with 4" bus for each phase (attached example). In which direction do the SC forces on each bus act? I am trying to figure out if any SC forces will make their way to the foundation or if they cancel out at the beam. Talking to one engineer, he mentioned that the SC forces...