Recent content by wschel

  1. wschel

    Motor stop start power efficiency and maintenance

    Most motors are rated for a limited number of starts per hour. Don't forget to take that into consideration.
  2. wschel

    AC Busbar DC Rated

    The circuit breakers MUST be DC rated. DC current is much harder to interrupt than AC since there is no zero crossing.
  3. wschel

    Required experience for PE exam

    As a former boss once said "He says he as 20 years of experience. Come to find out, he has 1 year experience, 20 times!"
  4. wschel

    independent vfd of 3 pumps feeding system at separate locations

    Could you provide more information about the header configuration? This has a significant Are the pumps connected to a single pipe (size?) at different points (How far apart?) or does each have a line meeting at some common point? What is the flow & pressure ranges? With a little more...
  5. wschel

    independent vfd of 3 pumps feeding system at separate locations

    Do you have a hydrostatic tank in the system? That & very slow acting controls should lessen the problem with pressure waves. Will there be any communications between pump controls? You'll probably need to use a combination of pressure & total flow in order to match the number of pumps to the...
  6. wschel

    broken / arc-damaged lug on motor surge arrestor ground jumpers

    electricpete, Has phase A cap been replace or removed? I have seen people bend lugs to get the conductor out of the way while replacing equipment. That could weaken the lug at just the point where it failed.
  7. wschel

    Breaker size

    Chances are the 500A CB is designed to serve only as a local disconnect switch at the MCC. The 400A CB serves as the overcurrent protection for the 500 kCM feeder. The idea being that the 400A CB would trip before the 500A CB. Of course for most faults, both CBs will trip. I have seen older...
  8. wschel

    Metric Cable Derating

    cuky2000 Thanks a lot. That's just what I needed.
  9. wschel

    Metric Cable Derating

    cuky200 Could you elaborate how the derating is calculated? Is the Neher-McGrath method used?
  10. wschel

    Metric Cable Derating

    Does IEC 287 or other IEC standards require derating Direct Buried 3/c Medium Voltage Cable based on thermal conductivity?
  11. wschel

    One Drive, two pumps

    Multiple pumps on a single drive was fairly back in the days drives cost an arm & a leg. The drive is set up with output contacts and interlock to switch between the 2 motors and uses closed transition transfer to accross the line after reaching full speed. They normally would not use open...
  12. wschel

    Power Cost Calculation: 600hp 2300V vs. 600hp 460V

    The cost differences are not so much is actual power used, but in the cost of installation. Do you have sufficient 2.4kV and 480V power close to the motor location? Will the a transformer be required for one or both voltages? You should determine what is required for each voltage, calculate...
  13. wschel

    Speed control in asyncronous wound rotor

    Speed of wound rotor motors is usually controlled by resistor banks, liquid reostats or energy recovery systems. I believe that you are looking for a solidstate energy recovery system that converts the rotor current and injects it back into the power system. A number of these system were...