Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Wirenut

  1. Wirenut

    HIGH VOLTAGE VARIATION ON MOTOR

    I have a motor running @ 10% above full load current and the voltage is 10% above motor name plate. What will happen to the current if I get the voltage to nameplate???? 40 HP motor 3 phase, 460 volts nameplate, Wirenut
  2. Wirenut

    Rad resistant E-Stop push button

    Contact these people http://www.spectrumtechnologies.net/ They will know.... Wirenut
  3. Wirenut

    PE Question - take the FE exam or petition???

    I passed the PE in April of 2001. I went around to some A&E's and was not too happy with what they had to offer. I recently started a job with a public utility and love it. I know I will never regret getting my PE!!!!!!!!!! I know that it at the very least opened many doors that would have...
  4. Wirenut

    motor drawing excess current

    PUT A 100 HP MOTOR ON IT. MOVE ON TO OTHER PROBLEMS.... Wirenut
  5. Wirenut

    Resistor sizing for regnerative loads?

    It is very possible that the drive manufactor would offer these resistors as an option. At least they will know how to size it. GET ON THE PHONE!!!!!!!! Wirenut
  6. Wirenut

    Any Advice on Dealing with "Look Good" Managers?

    Be invisible. Enjoy your life away from work. Get a hobby. Don't be a trouble maker. Do what your told at work. Conform. Live long and prosper. Wirenut
  7. Wirenut

    3 Phase Heater

    Before we are finished we will have you running 0000.... Wirenut
  8. Wirenut

    3 Phase Heater

    I was assuming you wanted the current from the source, which is the line current. I doesnt matter how the load is connected, the current for the feeder breaker will be the same. Although I have my PE, and have sized cable for industry and Naval ships for years, I am no expert in the NEC...
  9. Wirenut

    3 Phase Heater

    He did say THHN. I show 90 degrees C with an ampacity of 95 amps. Of course that does not take voltage drop or the fact that you would probably but a 100 amp breaker on the circuit. More than likely he would need but a 100 amp breaker and use #2 awg. Wirenut
  10. Wirenut

    3 Phase Heater

    86 amps is the current on each phase, 4 awg should work Wirenut
  11. Wirenut

    3 Phase Heater

    Using the formula AMPS=(KW x 1000)/(VOLTS x 1.73) I come up with 86 amps. Wirenut
  12. Wirenut

    cables

    WBD Thanks for the information. I have never thought of it that way before now. Wirenut
  13. Wirenut

    cables

    WBD... What you have said does not make common sense to me, however, I am very trainable. Please provide more detail on how the life of a cable is extended because of heating caused by load current. I have never thought of heat as a benefit to the life of a cable. I do agree with your last...
  14. Wirenut

    15kV Switchgear Creepage and Clearances

    Your answer does help. As I suspect, and you seem to agree that these distances can't just be looked up in a table. There are many factors to be considered. I can only say that there are no specific standards for this rather unique application. Wirenut
  15. Wirenut

    15kV Switchgear Creepage and Clearances

    When designing medium voltage switchgear (15kV), do any standards exsist in regard to minim creepage and clearance distances. Should these distances be a factor of envirionmental conditions, scheduled maintenance, etc. Does any one have any references on this subject. Wirenut

Part and Inventory Search

Back
Top