  1. wilkin

    inductance calculation

    how do you calculate the inductance of a multilayer coil are cored?
  2. wilkin

    3kV insulated CTs on 11kV cable!

    The cable screen is non magnetic and can therfore be left in place but the earth for the screen must be returned through the ct for earthing. With the cable earth screen intact the voltage level for the ct is .72/3kv. If the cable is not screened the air between the cable and the ct will...
  3. wilkin

    ADDING UP ALL 3 PHASE CURRENT IN A PANEL SCHEDULE?

    A 3 PHASE 400 AMP BREAKER CAN CARRY A MAXIMUM OF 400 AMPS IN EACH PHASE. THERETICALY FOR A BALLANCED LOAD AS EACH PHASE IS 120 DEG APART THEY AD UP TO ZERO.
  4. wilkin

    CT hysteresis losses

    In an AC field the flux reverses in direction during each cycle. energy is lost in watts for this cycle and appears as heat. If the cycle is interupted flux is left trapped in the core. When a new cyle is started this remanent flux will effect the new cycle. To prevent this when switching the...
  5. wilkin

    air core reactor

    hi does anybody know a formula for multi layer coil air core reactance. for use in calculating for toroidal and strait coils
  6. wilkin

    Stress on coil insulation volts per mil

    Air is difficult to iliminate from insulation as it is in tiny spaces within most materials. at 50 volts per mil these spaces will not discharge and cause breakdown. With special processing higher levels are achievable. Typical breakdown figures for air mm v/m 0.025 355.6 0.123 177.8 0.25...
  7. wilkin

    Electrical Steel curves and magnetizing current

    The basic formula for Voltage is E = 4.44fBsAN volts B = Peak FLUX DENSITY A = area N = turns s = space factor The constant 4.44 is 4 x 1.1 where 1.1 is the form factor for a sine wave. A square wave would be 4 x 1 = 4 E/4.44fsAN = B = Peak FLUX DENSITY. This may clear your vision ?
  8. wilkin

    Electrical Steel curves and magnetizing current

    The basic formula for Voltage is E = 4.44fBsAN volts B = Peak FLUX DENSITY A = area N = turns s = space factor The constant 4.44 is 4 x 1.1 where 1.1 is the form factor for a sine wave. A square wave would be 4 x 1 = 4 E/4.44fsAN = B = Peak FLUX DENSITY. This may clear your vision ?
  9. wilkin

    Long Protection CT Leads

    Sorry for maths error corrections as follows The MCSU burden at 8% setting is 0.03 ohms. The pilots are 21 ohms. The voltage developed is .08 x 1.9 x 21.03 = 3.2 volts 5VA CT 5P10 will be acurate to 1% of 1amp at 5 volts ie 0.01 amps(the actual current could be obtaind from a mag curve) The...
  10. wilkin

    Long Protection CT Leads

    Your calculations are well informed and accurate i would add the following comments The MCSU burden at 8% setting is 0.03 ohms the pilots are 21 ohms the voltage developed is .08 x 1.9 x 21.03 = 3.2 volts 5VA CT 5P10 will be acurate to 1% of 1amp at 5 volts ie 0.01 amps(the actual current could...
  11. wilkin

    Toroidal transformer leakage inductance

    The leakage flux in toroidal power transformer is negligable. The inrush current at switch on can be very high (limited by primary resistance only) if core saturates. To counter this the operating flux can be lower or a starting resister can be used. The fault current is limited by resistance only
  12. wilkin

    Transformer Voltage Drop

    BS171 OR ANY POWER TRANSFORMER SPEC GIVES A TOLERANCE BETWEEN THE DECLARED TRANSFORMER RATIO AND THE TESTED TRANSFORMER RATIO AT NO LOAD.THIS VALUE IS SMALL AND CHECKED WITH ACCURATE INSTRUMENTS.(1%)
  13. wilkin

    Insulation of cable from transformer neutral terminal (Y-point)

    IN THE UK THE GRID TRANSFORMERS THAT ARE SOLIDLY EARTHED 132 KV AND ABOVE HAVE 11 KV RATED INSULATION STAND OFF BUSHINGS THIS ENSURES THAT EARTH FAULTS FOLLOW A FIXED PATH TO EARTH VERY OFTEN THROUGH A PROTECTION CURRENT TRANSFORMER
  14. wilkin

    Underground LV cables

    The short-ciurcuit rating for a cables in parallel is only that of a single cable and this can cause problems with protection settings