  1. wilber

    White Residue on Cable Jackets at Paper mills

    I am trying to research a test for ozone resistance. There is apparently a history of a white film forming on plastic jackets of cables exposure to ozone and sunlight at the same time. This is said to occur at Pulp and Paper mills. Does anyone have any experience with this? I would like to...
  2. wilber

    Superconductors?

    There are several superconducting projects using liquid nitrogen. For super conducting cables and current projects check out http://www.ultera.net.
  3. wilber

    Lightning damage to underground sprinkler system

    Heavily shielded cables are use for airport lighting applications. The shielding is thought to help with failures due to lightning. check out http://www.mysouthwire.com This is advertised as "resistant", but not "proof"
  4. wilber

    Temperature of Lugs

    During operation (and testing for approvals), lugs should always run "cooler" than the conductor. If a lug is at the same temperature or a higher temperature then a failure is bound to occur.
  5. wilber

    IEC 227

    I am interested In cables made to IEC 227. The standard as available at IEC is apparently in Russian. The cable are made to a Chinese standard based on the Russian IEC 227. Does anyone know of a English version of this standard or a standard that it is equvalen towritten in English . The...
  6. wilber

    bulkhead fire rating

    I have been asked if a Underwriter's Laboratories Type MC cable will compromise a A-60,H-60 fire-rating of bulkheads when making a multi-cable transit (MCT's) when passing through them. This job is on offshore platform project near Kuala Lumpur, Malaysia. I am familiar with "through...
  7. wilber

    FORMULA TO CALCULATE DIAMETER OF BUNCHED ELECTRICAL CORES

    For cables of the same diameter There is a factor 1 cable Factor is 1 7 cables the factor is 3 19 cables the factor is 5 37 cables the factor is 7 61 cables the factor is 9 Cables all of the same diameter, formed around a central single core follow the "rule of 6" the first layer is 6...
  8. wilber

    Design of Electric Power Transmission Lines

    There is also a "Overhead Conductor Manual" book available from Southwire. http://www.mysouthwire.com/Southwire/cda/content/article/0,1443,121_691,00.html Is the table of contents you'll need to "sign in"
  9. wilber

    airport lighting cable sizing

    A good article on airport lighting cable can be found http://ecmweb.com/ar/electric_series_lighting_circuitry/index.htm
  10. wilber

    Experience with Distributed Temperature Sensing (DTS) on power cables

    The temperature that the fiber optic member is trying to measure should be compared to the rated temp of the cable. That rated temp is assumed to be the temp of the metal conductor. So the closer you get to the conductor, the better. However the manufacturing techniques of the cable...
  11. wilber

    cell phone use in buildings

    Be easy on me guys. I'm a Mechanical Engineer and I work for a wire manufacturer. Can the construction of a building enhance the performance of a cell phone. Can the placement of the normal power cables within a building enhance the performance of a cell phone. Is there an A&E or consultant...
  12. wilber

    Over Head Transmission Line

    There is an "overhead conductor manual" written by southwire http:/www.southwire.com
  13. wilber

    Protection/comms pilot cables in tunnels

    If you are wanting NOT to generate smoke in case of a fire, then don't use PVC. Investigate UL 1685 Standard for cables. This standard defines cables that pass the standard vertical ladder flame tests and carry an "LS" limited smoke rating. They are usually less dangerous fumes in...
  14. wilber

    I have a 185mm Al 11kV pair of cabl

    Insulated cables are rated by a certain ampacity to keep the conductor and insulation at the rated temperature. End devices and conectors are usually rated at a temperature below the cables temp. Usually the rated temperature of the devices are 75C and the cable is 90C. Nothing delterious...
  15. wilber

    Looking for URD Design Class or literature

    We have some literature at http://www.electricsmarts.com/catalog/catalog.aspx?rid=5&tid=7 There are also "catlog data sheets " at http://www.southwire.com We have both EPR and XLPE I'm at our technology center not the sales group.