  1. welshwizard

    motor efficency vs. power factor?

    The power factor issue only relates to ac machines The windings represent an inducitve load and this produces a lagging power factor a pf = 1 is perfect! and 0.9 is better than 0.6 etc The circuit must be capable of supplying this unwanted current so cables and switchgear must be sized up to...
  2. welshwizard

    help 16th edition wiring regs

    Sorry Jeremyd But you cannot get a free copy! I've just ordered 15 copies for my students and tried to find a free source Typical cost is about £45 and dont forget the IEE On-site guide at about £14 because not all the info is in BS7671 You can get a version on CD-ROM You may get some useful...
  3. welshwizard

    Insulation Systems, and double insulation ...

    Picking up on some of CurtBs points Single insulated hand tools etc require a cpc earth wire as the safety conductor If the earth wire breakes then the safety conductor is lost increasing the users risk of electric shock Double insulated tools do not require an earth wire as the protection...
  4. welshwizard

    Protective Coverings 600 V or less

    Dont forget the fuse must be able to withstand the prospective short circuit current (PSCC) and still operate safely
  5. welshwizard

    Shower isolation switch

    BS 7671:2001 the Blue copy of the IEE Regs Part 6 contains Section 601 which deals with locations containing a bath or shower The room is now divided up into Zones 0,1,2 & 3 according to risk when electricity and water meet Zone 0 is the interior of the bath or shower basin Each zone has a...
  6. welshwizard

    Number of sockets

    I can help if you are working in the UK
  7. welshwizard

    Shower isolation switch

    Insulated pull cord operated switches complying with BS 3676 are permitted in Zones 1 & 2 of a bathroom installation Reg 601-08 You can also mount a conventional wall mounted switch outside the door to control the bathroom light as an alternative option
  8. welshwizard

    XLPE Cable Cleating Spacing Distances

    If you are UK based Try table 4A Page 103 IEE On-Site Guide
  9. welshwizard

    RESIDUAL CURRENT FOR PERSONNEL PROTECTION

    In UK we rely on EEBADS to protect people & livestock against shock risk from indirect contact For circuits supplying socket outlets the protective device must disconnect the circuit under fault conditions in 0.4 seconds or better We can install a 30mA RCD on the circuit to provide protection...
  10. welshwizard

    transformer insulating oil..

    In the UK doing an electric strength test using the "withstand test" Ideal test temp 15C to 25C at atmospheric pressure Set gap to 4mm Fill container and start testing within 10 min Increase test voltage in 2kV steps upto 30kV for 11kV oil sample If test fails carry out two further...
  11. welshwizard

    IEEE requirements shower

    In UK circuit must have a 0.4 sec disconnection time Watch out for supplementary equipotential bonding A 30mA RCD can be fitter to reduce shock risk Read BS7671 Part 6 Section 601 for Locations containing a bath or shower
  12. welshwizard

    UK - Design Standards

    The main driver in the UK is the Electricity at Work Regs 1989 which is the statutory document Designing to BS7671 is considered a "good interperetation" of this set of Regs - BS7671 itself is not statutory For all UK electrical systems the statutory document is the Electricity as...
  13. welshwizard

    Tiger Ring Main Unit

    Thanks Bung Sorry Redwing it should read 1000kVA not 100kVA! Life is truly non-linear!
  14. welshwizard

    Tiger Ring Main Unit

    Hi Redwing its me again I've dug up the following info which may help solve your problem We used 90A Fuses ESI REF IIOIL10 in FRUM'S on 100KVA TX'S. Manufacture ref as follows B.S.= OQGRN 90A G.E.C = KEMXO 90A & Brush OHGMA 90A The max size LV fuse we would fit to discriminate was 600A The HV...
  15. welshwizard

    Earthing of dockside crane

    As you say lee5 TN-C or PEN conductors are not very common Do you need a neutral if the motor is a 3 phase balanced load or is the neutral required for a control circuit function? RCD's will not operate with a PEN conductor on their upstream side under earth fault conditions BS7671 has quite a...