Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by waross

  1. waross

    Upgrading Utility Distribution Transformer with an NGR

    When considering fault current levels, line to line faults are considered, not line to ground faults. If system upgrades increase the level of available line to line fault currents, then reducing line to ground fault currents does nothing to help.
  2. waross

    70:250.30(A)(1) Exception 2

    A bonding jumper in the service entrance switch?
  3. waross

    Probability Distribution of Transformer Inrush

    Note that this case applies when the transformer is the same capacity as the alternator. For a transformer of 1/2 the capacity of the generator I suggest using rated current times two, plus or minus 25%. For a transformer of 1/3 the capacity of the generator I suggest using rated current times...
  4. waross

    Heat treatment machine power supply issue

    Take the rated KVA times 1000. Divide by the rated secondary voltage to get the rated secondary current. The rated secondary current must be equal to or greater tha the losd current. Example: Transformer Ratings. 10 KVA, 480/120 Volts 10,000 VA / 120 Volts = 83.3 Amps. The 120 Volt windinhs...
  5. waross

    Upgrading Utility Distribution Transformer with an NGR

    As I understand the rules, fault currents are based on line to line faults, not line to ground or line to neutral faults. If they are impedance grounding distribution circuits I hope that the services do not include a neutral conductor. The last time I saw impedance grounding it was on the power...
  6. waross

    Heat treatment machine power supply issue

    You may find it educational to read other posts before posting. A number of your suggestions may be a little off. One instance; By far the cheapest, both cost of material and labour, is the open delta auto-transformer boost. Capacity depends on KVA, not kW. This connection inherently causes a...
  7. waross

    Spain and Portugal power grid collapse

    I'm waiting for a "Space Laser" conspiracy to develop. grin
  8. waross

    Probability Distribution of Transformer Inrush

    I would size the protection to withstand a very short transient of 25 times full load current and sleep well. But, that is for a grid tied system. For an islanded system you may wish to consider the following points: Your energizations per week or year may be many times what a large grid...
  9. waross

    Struggling to understand how Back EMF works in AC Motors

    Consider an induction coil or a transformer. A rising current in an induction coil, a transformer coil or in a motor winding causes a rising magnetic field. That rising magnetic field induces a voltage in the winding that is causing the magnetic field. In a motor, part of the magnetic field is...
  10. waross

    Excitation current on induction motor as a generator via VFD

    I once set up a demonstration for some students in a vocational school shop. A three phase induction motor coupled to a DC motor. I connected a resistor bank in parallel with the AC motor. I started the AC motor on the normal supply. Then I ran up the DC motor until it was over-speeding the AC...
  11. waross

    Excitation current on induction motor as a generator via VFD

    A question and a suggestion Jeff. Can they use the water to spin up the turbine or is there an issue with flow control? Suggestion; I am wondering if even a small excitation will boot-strap the motor and cause it to start self exciting? Will the VFD pick up the motor on the fly?
  12. waross

    Struggling to understand how Back EMF works in AC Motors

    In a synchronous motor the speed is fixed. The back EMF voltage is controlled by the excitation. At lower levels of excitation and back EMF voltage, the motor draws reactive power. As the excitation is raised, the back EMF rises until it equals the supply voltage. At this level there is no...
  13. waross

    Struggling to understand how Back EMF works in AC Motors

    Typically, full load = 1760/1800 = 40 RPM slip = 40RPM/1800RPM x 100 = 2.2% You are on the wrong track considering voltage. Voltage differences drive reactive current. Normally, the phase angle of the back EMF decreases as the motor speed increases. Phase angle difference is what drives the...