  1. warmulli

    REF SETUP ON TWO LV SWITCH PANNELS WITH ONE MCAG

    Hi Bill, Please see attached drawing i have added, it shows the transformer with the two LV supply’s coming off it feeding the two LV panels. Both LV panels contain a set of CT's and one panel contains the relay MCAG16 looking at both sets of CT's protecting the supply cable/transformer...
  2. warmulli

    REF SETUP ON TWO LV SWITCH PANNELS WITH ONE MCAG

    Hi Marmite, I have attached the drawings showing the two sets of CT's, you can see the neutral CT is missing. Regards http://files.engineering.com/getfile.aspx?folder=033b67fa-6f21-4ca1-a1de-44a1a4a216ab&file=ref.pdf
  3. warmulli

    REF SETUP ON TWO LV SWITCH PANNELS WITH ONE MCAG

    I have come across a REF setup causing some confusion, any help. Comments are welcome! Setup: One 11KVA transformer with two LV feeds supply two C&H LV Switch panels with one switch panel containing a interconnector supply another LV panel. The MCAG setup is as follows: MCAG relay located on...
  4. warmulli

    MCAG14 Restricted Earth Fault Tripping

    Thanks guys for you help and input, Shutting down soon for testing so will hopefully get a result. Tripping became more frequent as load has increased over time, making the possibility of a reversed polarity on the neutral CT also have notice the stabilizing resister setting have not be altered...
  5. warmulli

    Power Consumption formula

    Thanks Bill thats great.
  6. warmulli

    Power Consumption formula

    Thanks for you reply, A bit confused on the two methods. If you use the first method KVA = kv x current x 1.732 this gives a much higher KVA then the second method. Is there a reason for this?
  7. warmulli

    Power Consumption formula

    Hi, Can anyone help clear the air, I am trying to calculate the total KVA demand from a set of reading i took from a 3-phase supply. I used a power quality meter to record the max current reading from each phase. 120A 140A 143A, i am trying to convert the reading to a total KVA demand but...
  8. warmulli

    MCAG14 Restricted Earth Fault Tripping

    Hi Guys, Please could you help with any suggestions. I got a 1000kVA 11KV dry cast resin transformer with two LV panels connected to it. It has a MCAG14 on the interconnecting LV panel but also seems to have a set of CT's connect to the other LV panel, The REF tripped around a year ago which in...