  1. vtpower

    Old Cables

    Another option for older cables is something we have done recently which is Cable Cure Injection. The problem is, you need to take the cable out of service to inject them, but you don't need to replace. It will essentially rejuvenate the insulation, filling in any treeing that my have...
  2. vtpower

    Load Break Switch Grounding and Inspection Best Practice

    apower, The voltages range from 12KV to 34KV distribution. Often times we can not use switch grates do to the location, i.e. in town sidewalks, mowed lawn. On the transmission and especially in subs, we use the grates. The field personnell always wear gloves when operating switches, so the...
  3. vtpower

    Load Break Switch Grounding and Inspection Best Practice

    Hi Folks, I am at an electric utility and an item that has continued to come up at our Union Labor Management meetings is if we are doing adequate initial grounding testing and adequate annual inspections of Load Break Switches. I would be very interested to hear what people do for initial...
  4. vtpower

    Wood Pole

    Just FYI as well, a 750MCM, 15KV Riser on wood pole is a fairly commmon installation. There typically is not a whole lot of structural analysis that needs to occurr, unless you are talking an un-guyed structure. We typically use either 45' Class 3 or 50' Class 3 poles.
  5. vtpower

    Voltage Collapse

    dpc, As it turned out, once upon a time, someone had a the idea of inserting an automatic throwover scenario between two seperate sets of bus pots. In my exploration of the AC, DC schematics, I failed to recognize this. It turns out the relay that would do the transfer was dropping out and...
  6. vtpower

    Voltage Collapse

    Thanks, I am in the Northeast. I usually deal with George A. from SEL, but would greatly appreciate any contacts you may have to dig into this. Thanks
  7. vtpower

    Voltage Collapse

    Yes, there are three PT's connected phase to ground.
  8. vtpower

    Voltage Collapse

    We recently had a very large fault on one of our 34.5kV Subtransmission lines. It was a phase to phase fault (no ground involved), and the fault itself was about 11,000 Amps. As you can imagine there was contribution from a large number of sources, as it is a looped system. At one of the...
  9. vtpower

    Spacer Cable Saggind Data

    Howdy, I am looking for sagging information with regards to spacer cable, in this case Hendrix. I normally use Sag 10 and PLS Cadd for transmission line design but have not had to design underbuild with Hendrix Spacer. I assume I am mostly interested in the sag of the steel messenger, along...
  10. vtpower

    Voltage Imbalance on Long Three Phase Feeder

    Thanks for the responses. I had checked the line balancing a few weeks ago and the current un balance was very minimal. Also, the line to neutral voltages are all equal very well balanced. It is only the line to line voltages that being affected, which I believe should only be due to the...
  11. vtpower

    Voltage Imbalance on Long Three Phase Feeder

    Folks, I had posted a few weeks ago about a strange phase to phase voltage imbalance measured on the secondary of a three phase 12.47 x 277/480V transformer bank. We recently checked another bank further down the road and have the same issue, 208, 208 and 217. The 480 bank measured 480, 480...
  12. vtpower

    Small wind turbine in parallel with mains

    Every state has different net metering rules (assuming your in the US) Here, we allow customers to install a unit at their residence, such as a windturbine up to 15KW,and run in parallel with the system. As everyone has mentioned, if you are generating more energy than the house is consuming...
  13. vtpower

    480V Wye Service Voltage Issues

    wbd - The relay is actually set for 5% imbalance, so it shifts depending on the phase to phase voltages. The facility manager is looking into a similar relay with a 10% imbalance trip, but of course we still have the strange voltage issue that will cause motor winding heating. I am at Green...
  14. vtpower

    Circulating Ground Current on Cables

    Thanks for the respones. I am aware that this is not common practice to run similary phases in the same pipe. The pipes are all non-ferrous and do not have any ferrous material, i.e. condulators on them. I think we will end up having to do as Waross mentioned and isolate one end of the neutral...