I came across an air circuit breaker installed on main LV switchgear. The breaker type is CN2 4000A with trip unit as NLG.
As the breaker is discontinued, I am not able to find any details online.
Appreciate if anyone has any information about the breaker trip characteristic to use in ETAP module
Thanks. I have transformers 0.6/120-240V 25KVA, 37.5KVA, 50KVA, & 75KVA.
The IE values are not practical with ETAP results. ETAP is selected for single phase calculation method. I presume they use equivalent formulas. If I use transformer secondary fuses, then I can get more logical results. The...
I am performing Arc Flash for a plant with many small 15,25,27.5,50KVA center tapped transformers feeding LV Panelboards. The result from the Arc Flash Calculations are very High and probably not practical.
Is there assumptions made in this situations similar to LV 3-Phase system Like for...
I am licensed in Ontario as EE. I have to perform a job in Quebec and for that I will need Permit to work as engineer from OIQ, Quebec. As per OIQ, I can get temporary license for specific job, but I have to pass professional exam, for which they don't have any english study material, although...
I have worked on current impression systems for oil storage tanks to protect the bottom.
there are 2 ways that I have worked with.
one method is you use deep-well anode away from the concrete. You install anodes in the deep well, usually there will be anodes at different levels through a chain...
I would like to know if I need to change the fluke 435 default current Range 3000A to be close to load current or keep as is to start measurement as the manual suggest.
The panel I will connect has total load of 100A.
The transformer HV side CTs at SWG are 500/5A and LV side at TR are 800/1A. The Transformer is 5MVA 7.2x4.16KV.
Can the CTs be used for differential protection without interposing relays with GE 745
I have worked most of the time in persian gulf and in oil and gas projects. We always considered:
single pair cables with shield for analog and digital signals
multipair cables with individual and overall shield for analog signals
multipair cable with overall shield for digital signals
I am new...
Anyone can give input about specifying instrument cables for power plants. The cables will be for:
-Analog input 4-20mA or RTD
-Digital Input/output
-Input/Output cables from Swicthgear to PLC for control and monitoring
I am looking specifically whether to provide shield on Digital input/output...