  1. UKEng

    Arc Flash - NFPA 70E

    Scotty, I am a UK Engineer working in the Oil & Gas sector. We are in the process of purchasing SKM PowerTools to carry out our study. We will be using the arc-flash module as previously described. We have made contact with PPE suppliers in this area and are moving forward with the project...
  2. UKEng

    HV Protection Training

    P&B Engineering in Manchester do an excellent 3-day course that will suit your requirements. regards
  3. UKEng

    3.3kv Motor Earth Fault Setting

    jbartos, After further ivestigation, please find the following. The original design was done in Japan and approved in Japan. Apparently this is the standard earth fault setting over there. Alstom built and fitted these components as per design. I rang Alstom UK and their recommended...
  4. UKEng

    3.3kv Motor Earth Fault Setting

    Kiribanda, The 3.3kv system is resistance earthed which limits the earth fault current to approx 400A. We used a single phase injection set and passed the test lead through the centre of core balance CT and raised the current until the relay tripped. The earth fault has a time delay also. The...
  5. UKEng

    3.3kv Motor Earth Fault Setting

    Hi All, I am starting to commission a new chemical plant and have come across the following. Motor Volts - 3300v Motor FLA - 106A Motor Protection - Gemstart 4 Normally I would accept the Earth Fault Setting from betwwen 10% - 20% of FLA, in this case approximately 10 - 20A. We primary...
  6. UKEng

    Equivalent star reactance

    On a cable 'electrical characteristics' sheet what is meant by 'equivalent star reactance per 1000m of cable at 50Hz'. i.e. what is the star reactance. many thanks
  7. UKEng

    Ultrasound application on switchgear

    I have not used this this method myself but have heard from other Engineers who use this as part of their routine maintenance. Apparently it is no use at lower voltages but is useful at voltages of 3.3kv and above. The benefit is that it is non-intrusive and gives a good indication of partial...
  8. UKEng

    IEC 60079-17 - continuous supervision

    In the standard for Inspection and maintenance of electrical installations in hazardous areas, what is meant by 'continuous supervision' and in what instance would it apply?
  9. UKEng

    DC Ground Faults in a Power House

    I forgot to add this link http://www.hi-potential.com/products.asp?ID=8
  10. UKEng

    DC Ground Faults in a Power House

    The DC earth fault locator is known as a 'Grouser'. I believe it injects an 11hz signal into the cable and is traced using a horseshoe shaped pick up unit.
  11. UKEng

    Generation Question

    Thanks bigamp, a star for you. Would it be possible for two or more generators to be run in Isochronous mode or would you you only have one of them in this mode. thanks
  12. UKEng

    Generation Question

    Could someone please explain the difference between 'Isochronous mode' and 'droop mode' when talking about two diesel generators connected in parallel on it's own common bus and not connected to a utility. Which method would be the best way to run these. many thanks
  13. UKEng

    What is Field Flashing

    Hi, Could someone please explain the term 'field flashing' with reference to generators. What is it and how is it carried out. Many thanks in advance PaulUK
  14. UKEng

    Generator Fault Levels

    Hi All, What are typical values of fault levels for generators with respect to their ratings? Also could someone explain what is meant by saturated and unsaturated conditions. Many thanks in advance Paul