  1. TSDavis

    RPZ Backflows in Pump Suction

    Although not part of the actual standard, A.4.7.2 says...... "It is not the intent of this subsection to restrict the use of pressure reducing valves downstream of the discharge isolation valve for the purpose of meeting the requirements of 4.7.7." So in essence, once you've passed the pump...
  2. TSDavis

    Metal parts in plastic bin boxes

    Yes but "High Hazard Commodity" doesn't mean anything. The IFC might as well have used the phrase "extra super gooder". It's doesn't point towards any particular criteria from NFPA. Well, not that I'm aware of at least. I think exposed, non-expanded, unstable, group A plastics to 12' with up...
  3. TSDavis

    Metal parts in plastic bin boxes

    Do I treat this as plastics storage? Looks like the bins will be stored to a max of 12' with 14' ish clearance to the deck. Feels like the bin boxes themselves are the hazard and not the product. Surely NFPA has addressed the plastic bin boxes being dictated by the auto makers. Terry S...
  4. TSDavis

    EC design area

    Bar joist construction, open shop, brass uprights, ordinary hazard 2, 22' deck height. Just a plain Jane type install. Terry S. Davis National Fire Protection h2o-racing@comcast.net
  5. TSDavis

    EC design area

    I've always thought my remote area for EC sprinklers was 5 sprinkler or 1500 sq.ft. Which ever is greater. Assuming no area reduction of course. Think uprights at 20' aff for OH. We've had an inspector tell us that if the sprinklers are protecting say 18'6"x18'6" and the flow is increased...
  6. TSDavis

    Apt. Sprinkler Design Area

    Your certainly right on that one. Very difficult to get info on fire sprinklers. It's like a black art. I was thrilled to find this forum to bounce ideas off of. Every once in while I find something in a standard that makes no sense. Then what? We rarely have time to wait for an...
  7. TSDavis

    Apt. Sprinkler Design Area

    Perhaps I have been fortunate. Would a TIA to the 1999 edition apply to previous additions of NFPA? Terry S. Davis TriStar Fire Protection tdavis0114@comcast.net
  8. TSDavis

    Apt. Sprinkler Design Area

    Strange. I posted to this and it's gone. You only need to provide the .10 gpm/sq.ft. in areas that are not dwelling units or their adjoining corridors. Discharge rates in the dwelling units and the adjoining corridors (if res. sprinklers used in corridors) "shall be provided in accordance...
  9. TSDavis

    Water Demand - Pipe Schedule vs. Hydraulic Methods

    Once you understand how it works you start to lay your systems out so that they balance. It's really fun with some of the programs available now. You can try different sprinklers, different pipe, different areas. Minutes to do what once took days. You can play with a pipe sizes, hit the...
  10. TSDavis

    Apt. Sprinkler Design Area

    You can use residential sprinklers within the dwelling units and the adjoining corridors and calculate just 4 sprinklers in accordance with the sprinkler manufacturers data sheet and NFPA13 Start with the definition of "dwelling unit" Then go to 5-4.5.1 7-9.2.1 This appears in the 1996 and...
  11. TSDavis

    Water Demand - Pipe Schedule vs. Hydraulic Methods

    Hydraulic calculations and systems designed with hydraulic calculations require an understanding of the effects the layout can have on the demand. A poorly designed system can have a higher demand than a pipe schedule system. I've noticed with some of our newer designers that they don't...
  12. TSDavis

    PVC in High Rise Buildings

    Another consideration regarding PVC piping on the upper floors is that the pipe itself requires much more hanger support. Sometimes the spacing of the steel is such that it becomes larbor intensive. You can use drop in anchors (if the spec allows it)but still there will be many of them.