Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations Ron247 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by TRAK.Structural

  1. TRAK.Structural

    Residential Load Bearing Wall Removal (A basic task & possibly an ignorant question.)

    There are some detailing considerations. Flush beam vs. dropped beam. If flush, are you cutting through ceiling joists that act as a tension tie for the roof? Proper detailing for disturbed elements with flush beams can sometimes be hairy. I almost always put new foundation supports under the...
  2. TRAK.Structural

    Composite Steel Deck

    I'd probably put a support out there. If nothing else it will help to firm it up during construction. Maybe you could use a steel angle (similar to a pour stop but more substantial).
  3. TRAK.Structural

    Legal Thoughts on Stamping Plans

    This is similar to how I would handle a residential plan set from an arch/designer. Typically I would use a blank plan layout as a background on my own sheets and add all the structural info needed (framing sizes, notes, details, etc.) And yes, clearly define what my seal covers.
  4. TRAK.Structural

    Multi-storey steel column bracing

    What will the connection look like where you change column sizes? Not sure what type of structure this is, but I've typically seen the column splices placed a few feet above the floor level. If you think the out of plane shear in the beam/col shear connections is too much for that connection...
  5. TRAK.Structural

    HUD Foundation Inspections

    I do these from time to time. Most of the time they don't meet the requirements and I stand my ground about what needs fixing. If you are familiar enough with the guidelines, get paid in advance, and don't mind crawling around in a dirty space below the homes than it's fairly easy work.
  6. TRAK.Structural

    Stacked Stone/Rubble Foundation

    Good points. Wouldn't repointing have the same effect though, considering that matching the existing mortar is not realistically going to happen?
  7. TRAK.Structural

    IEBC Allowable 5% Gravity Increase on Total Load or Load Type?

    I would still interpret it as meaning a maximum of 5% increase in the total load effect.
  8. TRAK.Structural

    seismic supports straddling building expansion joint

    I would think the ducting should have specific joints that can accommodate the expected movement across the bldg exp joint where the duct is perp to the bldg joint. I would avoid having the supports straddle the exp joint like shown in the middle of your plan layout. Can you use and inverted...
  9. TRAK.Structural

    In the ACI 350-20 Code, what is the purpose of the additional rebar spacing checks found in Section 11.9.9.5

    I haven't used this version of ACI 350 before, but the first part of section 11.9.9.5 reads as this is only for shear reinforcement? Only in unusual circumstances have I used reinforcing for shear in concrete water bearing structures; the concrete thickness itself can be sized to handle the...
  10. TRAK.Structural

    Is it possible to build classic precast pre-tensioned data centers in seismic zones ?

    I've done data center work in the past. In my experience the client has always selected sites to avoid seismic detailing, mostly SDC A or B. Data centers can have extremely heavy floor loads due to the server racks and all the mechanical/electrical equipment. Especially with multi-story...
  11. TRAK.Structural

    Cutting Door Opening Through Existing Precast Siding Panel

    If they are prestressed I think you need to know the arrangement of the tendons. Maybe scan the panel with GPR if you can't get record drawings. I've used the scheme with steel jambs/header like you mentioned before, but with conventionally reinforced concrete panels.
  12. TRAK.Structural

    Seismic Force When Designing Shear Friction

    As @KootK mentioned, all of the shear has to be considered when checking the connection of the superstructure to the foundation elements (and for global sliding, overturning, etc.) Mass from the lower half of walls should be resisted at the base of the contributing wall though, not distributed...
  13. TRAK.Structural

    Concrete Column - cold joint cracking

    Before telling them to tear it down and rebuild, you could require them to chip it back to sound material to see how much of the section is actually affected. Then you can make a determination on what to do.
  14. TRAK.Structural

    Anyone Ever Spec'ed these Joist Reinforcers?

    I've spec'd the Metwood one before. Never saw the install, but no complaints since. Don't they test them to get the approvals? This way you have actual performance data instead of just theoretical calculations.
  15. TRAK.Structural

    Stacked Stone/Rubble Foundation

    Figures. May float the idea of mortar testing, expecting raised eyebrows from the contractor.