Recent content by tolin

  1. tolin

    Effects of field forcing on fault currents

    Field forcing is used in case the generator is taking its excitation power from its own line side. In case of a short circuit near the generator, the voltage will decrease to zero, the field too and by that the short circuit current. In order to maintain short circuit current at a high level...
  2. tolin

    ANSI C2 and clearance in a 230 kV system

    I am a littel bit confused regarding all the tables listed in ANSI C2. In table 235-6 the clearance in any direction from line conductor to support arm is listed to 1240 mm. This value conflicts with the requirement to electrical clearance, 2150 mm (IEC 2100 mm) according to table 232-4. Can...
  3. tolin

    230 kV O/H Line Steel Towers

    Is there any American or Panamania standard, requirements or recommendations for steel towers used for high voltage circuits. I intent to connect a new 230 kV substation to an existing 230 kV overhead line at an existing suspension, tangent steel tower. Because of the cut and connection, we have...