Thanks. If there is a SLG on the HV side - in this case 0.5kA, does this 0.5kA then go back to the neutral of the star side of the HV winding only?
Does the 0.5kA HV SLG fault affect the LV side at all?
may be a silly question from me - wouldnt the 20kA SLG at LV side - most of the fault current will return via the earthing cable and then via the MEN back to the neutral of the generators being the source?
Hi,
I am looking at a pre-existing electrical system which is an off-grid microgrid.
This consists of 3 off low voltage 415V 500kVA generators feeding into 1 off 2000kVA 415V/11000V step up transformer to then connect to 11kV infrastructure for a small village.
The 3 off generators at LV...
Hi everyone,
I am wondering for those of us who are based in Australia, could we use the calculation methodology as per HB101 and HB102 for AS3835 to evaluate the AC induction voltages for a pipeline?
The AS3835 is titled "Earth Potential Rise - Protection of telecommunications network users...
Hi all,
Where we use X90 and X110 rated XLPE cables and we "push" the cables to run at a higher ampacity with a higher conductor operating temperature, say we take 80deg in this instance.
If we run these cables in PVC conduits (typically buried in-ground), would these PVC conduits not be an...
Thanks VTer. If I calculate the value using the formula you mentioned, i.e. 400A/3 x 11kV x Sqrt(3) = 2540kVA. Surely that is too big a size?
Thanks RRaghunath. I also think the IEEE is a bit more correct - but I am not sure why there is such a big discrepancy with the Westinghouse T&D which is...
Hi all,
I am trying to size the kVA rating of the zigzag TX. The parameters are:
11kV, Ineutral = 400A, 60sec rating.
Based on Westinghouse T&D book, the rating is calculated to be 11kV/sqrt(3) x 400A x factor of 0.104 = 264.2kVA.
Based on IEEE C62.92.4:2014, the rating is calculated to be...
Happy new year 2021 to everyone.
In the CDEGS FDIST module, I want to define a terminal using underground 11kV cables. I am trying to get to the user interface where it shows the following (the screenshot below is taken from the manual) but I could not find a way how to get to this screen...