  1. TECMSC

    Cost Savings - Reducing Condenser Approach Temperature

    sorry for the late response, I was away for awhile. quark - i would think the mcpdt equation can still describe an aspect of the situaion - the heat rejection stays the same then the mass flow increases(corresponding pressure increase)and refer DT decreases due to higher refregerant velocity...
  2. TECMSC

    Cost Savings - Reducing Condenser Approach Temperature

    We're considering some work to reduce the condenser approach temp. e.g 6°F to 1.6°F. In order to move forward I need to calculate the cost savings. The system has a water-cooled centrifugal chiller. Can the cost savings be calculated by using site data e.g. gpm, temperatures, power cost...
  3. TECMSC

    Heat rejection: Air Cooled Chiller vs Cooling Tower

    sridhar1312 - . WB depression seems to make sense, but unfortunetly, i don't have the exact temps during the summer months. CTDon - Thanks for the link - good info. Equalizer lines have been an issue in the past as well e.g. two cell towers -- 10"-10" into 10" then into 10" common equalizer...
  4. TECMSC

    Heat rejection: Air Cooled Chiller vs Cooling Tower

    HVAC68 - the design WB is 68°F. At 95°F DB and above the CWS temp starts to increase. I'm not sure of the WB temp but "typical" WB temps at 95°+ DB for our area. I think the issue is really a load based problem (need more heat rejection area as you indicated) at the towers and not so much...
  5. TECMSC

    Heat rejection: Air Cooled Chiller vs Cooling Tower

    Thanks HVAC68 for the spreadsheet cdxx139 - no problem with topic. this is good info and could figure into the decision in the long run (not to mention other projects!). for a little more info: we ended up adding louvers in adjacent walls and velocity stacks just to maximize performance of...
  6. TECMSC

    Heat rejection: Air Cooled Chiller vs Cooling Tower

    The desert would be nice! We inherited the site so had to make do with what was installed. Good point-will look into this as an option as well.
  7. TECMSC

    Heat rejection: Air Cooled Chiller vs Cooling Tower

    thanks everyone, i'll try to summarize: the plant is less thatn 10years old and is a total of 2000 tons (3+1 with 500T chillers/towers). The cooling towers are sized for 68°F WB (a little undersized). maintenance is good and the plant is running well, the CWS temp starts to rise when OAT rises...
  8. TECMSC

    Heat rejection: Air Cooled Chiller vs Cooling Tower

    We're considering two options for additional heat rejection. The problem is that on a design day our cooling towers run at their limits and we lose redundancy with them. The thought is to either add a 1000ton cooling tower to the existing ones (largest we can fit); or, add a 350 nominal ton...
  9. TECMSC

    Damper Leakage Calculation

    quark - DETAILS!! :) I appreciate your input and follow up. Thanks all.
  10. TECMSC

    Damper Leakage Calculation

    MintJulep - I agree it is best to fix or replace the dampers. There are multiple 130ton units and the cost would be signifcant and potentially disrupt operations. This calc may assist in quantifying the energy waste etc to present a case to fix, replace or seal them off. Quark - After I...
  11. TECMSC

    Damper Leakage Calculation

    Thanks all for the input. marc/utility/mint -- Damper Specs: I need to dig up the specs but I believe design should be less than 2 cfm/sqft leakage. In this case, we know they leak and are trying to determine if leakage is excessive and could potentially de-rate the unit on a design day e.g 105...
  12. TECMSC

    Damper Leakage Calculation

    Hello All, I was trying to figure out the amount (CFM) of outside air leaking through a closed control damper. After some thought it seems the best method is to calcualte the outside air percentage based on temperatures per the following: x% = outside air percentage (OA%) Ta = outside air temp...
  13. TECMSC

    Battery Room - Humidificaiton Requirement

    Thank you both very much for the response. GMcD...these are flooded batteries. we have proper ventilation rates and have not had any problems with static discharge and no humidification for the last five years i.e no explosions. gepman...To control the battery environment to a minimum of 30%...
  14. TECMSC

    Battery Room - Humidificaiton Requirement

    I've searched for a design guidline for humiditiy requirement in battery rooms but have not had any luck. There is quite a lot of info regarding ventilation but not humidification. What is a typical guidline or reference for humidity in battery rooms?
  15. TECMSC

    Chiller Oil Heaters on UPS Power

    mintjulep I'd have to verify the accumulator-I think it would be integral to the chiller. also, if the heater came on as soon as the generators kicked in (15seconds?) then we shouldn't have a problem with oil migration to the crankcase (although we would still have a longer reboot time for the...