Recent content by swz202

  1. swz202

    Cable Tray Clearance to Wall Requirement

    In Canadian Electrical Code it requires 600mm horizontal clearance between cable tray and wall (12-2200(6)), but in reality I've seen a lots installations that do not meet this requirement. Not sure what is the requirement in NEC, but I am wondering if anybody can explain if there are any other...
  2. swz202

    Distance between underground circuits?

    Try to answer your second question: First,CEC diagram B4-1 doesn't show 3 or 5, 7...paralell runs at all, it just shows different senarios of 1/2/4/6 paralell runs. Second, diagram B4-1 is intended to be used together with table D8A/B--D15A/B, to give you the maximum allowable conductor...
  3. swz202

    Relay Tolerance and Setting Errors

    0.25 cycle = 0.00417 sec, isn't it?
  4. swz202

    Liquid cooled or air cooled generator?

    Very helpful replies. Thanks you all.
  5. swz202

    Liquid cooled or air cooled generator?

    For a 750kVA standby generator, which is more common? Liquid cooled or air cooled? Liquid cooled will cost more, but how much more? Thanks.
  6. swz202

    Electrical equipment life span?

    I'm going to spend a couple days there to do some site investigation and inspection. At this point I have little information about this plant. Thank you guys all for your helpful information.
  7. swz202

    Electrical equipment life span?

    I am presently working on the evaluation and cost estimation of upgrading a 40+ years old gas plant. Want to have some idea what is the normal life span of transformers, switchgears, motors, cables, etc. Thanks in advance.
  8. swz202

    Help with finding an electronic variable resistor

    oops...i totally missed the power requirement part. I agree with Skogsgurra's resistors + contactors + PLC solution.
  9. swz202

    Help with finding an electronic variable resistor

    Try Analog Devices, http://www.analog.com/ and search for "variable resistor"
  10. swz202

    Power Cable Insulation Rating Question

    Another thought on this issue, we'll use 1000 volts rating cables for this application. Following is from IEEE Red Book: The selection of the cable insulation (voltage) rating is made on the basis of the phase-to phase voltage of the system in which the cable is to be applied, whether the...
  11. swz202

    Power Cable Insulation Rating Question

    We have a 600V ungrounded delta system. Is power cable with 600V insulation rating enough for this appilcation? My thought is, under a phase-ground fault condition, the other two conductors will subject to overvoltage.....
  12. swz202

    Wye Wye Transformer connection Pros and Cons

    I'm reading Handbook of Practrical Electrical Design by J.F. McPartland & Brian J. Mc Partland. Page 445: Wye-Wye transformer connections should generally be avoided because of the objectionable characteristcis of such connections. First, a connection of this type generally requires that the...
  13. swz202

    Circuit Breaker sizing for VFD and soft starter circuit?

    Thanks, Jraef, Do you mean I can size the circuit breaker of soft starter circuit the same way as in full voltage starter?
  14. swz202

    Circuit Breaker sizing for VFD and soft starter circuit?

    Does anyone know of how to size the circuit breaker for VFD and soft starter circuit? The code does not mention anything about it. Normally VFD user manual will give the suggested circuit breaker size. But what about soft starter circuit?