Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by submonkey

  1. submonkey

    Frame Leakage protection: 3 phase fault

    Hi Prot123, The 10 ohm figure was an internal utility requirement. Unfortunately I'm not aware of any public documents which list a frame insulation resistance. New switchgear installations designed for FL were mounted on an insulating mat and achieved far better than 10 ohms. Some FL...
  2. submonkey

    Frame Leakage protection: 3 phase fault

    Hi Prot123, A major Australian utility where I used to work applied earth leakage protection quite extensively on double bus 11 kV metalclad switchgear. Frame leakage was used because of the difficulty of applying high impedance protection on a board where breakers could be racked to either...
  3. submonkey

    Standards Relevant to Transformers

    Hi PRC, This is a very useful document - thank you for taking the time to write it, and for being so generous with your knowledge. Alan
  4. submonkey

    Bus Bar protection relay operated

    Hi, The oscillographic fault records in the 7UT6 will almost certainly confirm: (a) Whether the switchgear is likely to be healthy. (b) The probable cause of the trip. Download the records with DIGSI and get an appropriate person to have a look at them. Thanks, Alan
  5. submonkey

    Protection of Air Core Dry type Reactors connected to a Transmission Line

    Hi Hans, This is a very interesting problem. My previous employer used air cored reactors fairly extensively, and I did spend some time considering how to protect them. I generally dislike the idea of discounting certain fault types just because those present can't envisage how they might...
  6. submonkey

    Protection of Air Core Dry type Reactors connected to a Transmission Line

    Hi, A few questions:- Is the reactor at one of the line ends, or somewhere in the middle? Will it have an earthed or unearthed starpoint? What kind of line protection are you using? Is optical fibre comms available? Thanks, Alan
  7. submonkey

    any suggested online courses?

    Hi, These used to be available by distance education, and the one course I did was pretty good: https://www.qut.edu.au/study/short-courses-and-professional-development/short-courses/postgraduate-electricity-supply-training-course-pestc Thanks, Alan
  8. submonkey

    Switchgear Low Impedance Vs High Impedance Bus Differential

    Hi Rockman, The factors in favour of high Z are in my opinion: - Simpler to set, configure, prove, debug. - Very long life - the CTs and wiring will last as long as the switchgear. - If you use an electronic relay, you may need to factor in one replacement, but it is a simple...
  9. submonkey

    feeding 40km circuits on 33kV

    Hi, I agree with waross regarding the loss relationship. To make a sensible decision, I think you should model the system using a load flow program (or excel if you're desperate). It seems that you have option (1): run with 36kV at the sending end and, say, 33kV at the receiving end or...
  10. submonkey

    feeding 40km circuits on 33kV

    Hi prismpower, I believe that 36kV cables can sustain 36kV continuously, based on the definitions for "highest voltage for equipment" in the IEC standards. You may want to check the applicable standards if you are not in IEC land, and/or confirm with your cable manufacturer. A potential issue...
  11. submonkey

    Industry Practice for Programming/Testing Protection Relays

    Hi mbk2k3, The utility where I worked would always re-test (by secondary injection) the full function of a relay after re-loading a setting file. If the wiring was untouched, testing to links or a tripping (lockout) relay was sometimes accepted depending on circumstance. With modern relays, it...
  12. submonkey

    I have a question I have a CT with

    Hi, You can't do that. There is one continuous secondary winding on the CT with taps at 40 turns and then 60 turns. The primary has one turn. The (amps * turns) on the primary needs to equal the (amps * turns) on the secondary, and if you attempt to use both ratios at once, the amp turns won't...
  13. submonkey

    CT Open Circuit

    Hi Scottf, If the CT, the load, and the system were ideal (which they are not), the output voltage of the CT would be proportional to the system voltage. The primary of the CT would behave as an open circuit, because the CT would have a infinite magnetising impedance and all of the system...
  14. submonkey

    CT Open Circuit

    Hi A CT behaves the same as pretty much any other transformer - the difference is in how the CT is connected. Suppose you have a 2000/1 CT which is open circuit and connected in series with an 11kV supply. The CT secondary is open circuit, so the primary "tries" to behave like an open circuit...
  15. submonkey

    SEL-421L vs 311C and 311L

    Hi David, There was no bus differential - the utility which originally built the sub chose to rely on remote protection. After a number of faults (and replacement of breakers with ones containing BBP CTs) a project was eventually justified to install bus protection. Thanks, Alan