you are right.
unfortunately, I have often seen bladder tanks located inside warehouses protected by sprinklers.
so according to DS FM 04-12 all points must be respected, from A to D.
thanks
Thank you.
The DS FM 04-12, on the other hand, seems to allow installation in the protected area under certain conditions.
2.2.1 Equipment Location
2.2.1.1 Locate storage containers (e.g., foam concentrate), water tank, compressed gas cylinders,
proportioning equipment components, pumps...
According to NFPA 11:2024, is it possible to install a foam bladder tank inside the warehouse protected by sprinklers?
4.3.2.1.1
Foam concentrates and equipment shall be stored in a location not exposed to the hazard they protect.
Thank you for the comparison
According to NFPA 13 (2022 edition), what type of sprinkler protection is recommended for polyurethane foam blocks stored on roller conveyors?
The roller conveyors, similar to shelves with multiple storage levels, are intended for the curing of the blocks of polyurethane foam.
The material is...