    Resistor in the field winding circuit of a brushless exciter

    jbartos I don't have access to the handbook. Can you please explain it?
  2. sngpl

    Resistor in the field winding circuit of a brushless exciter

    Can anyone please let me know the purpose of a 22 ohms resistor in the rotor field circuit?
  3. sngpl

    #rd Harmonics from Steam Turbine Generator

    Try to measure the per phase winding resistance and also, if possible, the split phase winding resistance in order to make sure that all the phases have the same resistance. This is to see if there were any wrong connections made during the rewind.
  4. sngpl

    Test result comparisons

    thanks jplinn But I still am interested in knowing how to divide generators into groups based on for example MW, insulation class, etc.... for comparison of test results with in that group. I would appreciate any input in this regard.
  5. sngpl

    conversion of a 800A CB to two 800A CBs to prevent frequent tripping

    I guess a better approach would be to get a bigger properly sized circuit breaker!
  6. sngpl

    #rd Harmonics from Steam Turbine Generator

    It certainly appears that the harmonics are due to the way the generator has been rewound. However at this point I may add that there could be two major external sources of harmonics; 1- excitation system, 2- station battery charger because both have rectification equipment. Is it possible to...
  7. sngpl

    Test result comparisons

    Normally the test results of a piece of equipment are compared with its previous tests and also with test results of similar equipment. Would it make sense to compare it with the same kind of equipment but with different specifications? For example if we have a 10 MW, 13.8 kV, insulation class...
  8. sngpl

    PERIODICAL REVERSAL OF ROTOR SUPPLY POLARITIES

    jbartos: Can you please elaborate?
  9. sngpl

    Auto CAD and PLC programming

    I am intrested in getting Auto CAD and PLC programming training. Any recommendations for good institutes in Canada?
  10. sngpl

    PT Fuse Failure

    The megger results for the generator are really good and almost the same as the last test in performed in May 2003. We haven't yet operated the unit but hope that it should be fine. Thanks for all your suggestions, replies, information and suggestions.
  11. sngpl

    PT Fuse Failure

    X2K3 (Electrical) "PT connected in open delta should have one[middle] phase grounded. Was the ground connection intact?" I would rather disagree... Pts connected in Y have their Y-point grounded but not PTs in open delta. Please feel free to correct me, if I am wrong?
  12. sngpl

    PT Fuse Failure

    DanDel What I meant by not blown completely was that the 95% of the casing was still in tact.... normally its just shattered completely!! It was open of course.
  13. sngpl

    PT Fuse Failure

    rbulsara (Electrical) The PTs are in open delta for voltage regulation. The generator was not developing voltage. jbartos (Electrical) Can you please explain the phenomenon of ferroresonanne and its effect on the fuse in a bit more detail. Sounds really interesting. DanDel (Electrical) The...
  14. sngpl

    PT Fuse Failure

    We have a 3.6 MW Hydro Electric Power Generator. The unit was shut down for a couple of days and when we attempted to start it, it won't develop voltage. We found that one of the generator PT High Tension side fuses was sort of blown. I said sort of because it’s damaged in the center. I think if...
  15. sngpl

    TEG

    I need some good links explaining the working of Thermo Electric Generators (in which a bi metal junction is heated to generate electricity). I would appreciant all help. Thanks