    Power Sstems Software

    I would like to know of any Colleges or Universities in Toronto who would offer course in software used in Power System Analysis like ETAP etc.
  2. Siddhuca

    Parallelling Substation Transformers

    I would say most of the utilities in the Southern States of India were I worked have Transformers in parallel. Only when their impedences did not match, or the OLTC was not the Master slave type(to prevent transformers go out of step)the transformers were individually operated. We had...
  3. Siddhuca

    Parallelling Substation Transformers

    I speaking from practical experience.It is very usefull for even distribution of load among transformers.Some feeders may be loaded higher than others.Paralleling helps distribute the load and better volatge regulation on the overloaded feeder
  4. Siddhuca

    Big blackout. What happened?

    I have been reading all the comments in this forum. I find it extremely unbelievable that when the same 345kv line tripped twice , it was reclosed immediately without analysing the cause of the fault. Having two hours after the first trip "with good communication and instructions from a...
  5. Siddhuca

    Could the SC calcs from Th Cooper B

    Yes it seems the tables are for voltages for 600v. Could we calculate C values using standard ohms/feet values from IEEE stndards. "C=1/ohms per ft"
  6. Siddhuca

    Could the SC calcs from Th Cooper B

    Could the SC calcs from Cooper Busman method for point to point SC calcs used for HV substations instead of p.u method.