  1. Shophound

    Fan Law - Belt Drive vs Direct Drive

    There may be some savings in the direct drive since you no longer have losses via the belts. The belt drive assembly must have enough force to spin the motor sheave, belts, and fan sheave, along with attaining the desired speed of the fan or blower wheel to deliver the desired CFM. There is no...
  2. Shophound

    Estimating cooling tower energy savings using bin data

    Another caveat is local wet bulb data and the approach temp of your towers. If you lock in 70 degrees entering condenser water temp (ECWT) 24/7, on certain days of the year, the towers may not provide 70 degrees when outdoor wet bulb temps exceed 70 degrees. So your fans run flat out and...
  3. Shophound

    Understanding HVAC symbols in cad drawings?

    It is the symbol for sound attenuation.
  4. Shophound

    Small Chill Water System

    Also, have you thought about not completely unplugging from the chilled water supply of the building's central plant? In other words, if your little 3 ton resi condenser craps out, would you have the ability to switch over to building chilled water to tide you over until the three tonner is...
  5. Shophound

    Small Chill Water System

    Two challenges with running a resi/light commercial condenser in low ambient conditions: oil return and head pressure control. Fan cycling wears the condenser fan motors out more quickly. There are single phase controls that can turn the condenser fan into a variable speed, responding to...
  6. Shophound

    Creating a load on chilled water pipes

    How do you plan to circulate the water in the loop with no air handler coils in place? Is there a bypass? If so, is the bypass near the chiller or out in the loop, away from the plant? Has this chiller also sat a long time? How are its tubes in the condenser and cooler? Sitting a long time can...
  7. Shophound

    single family residence in southern calif

    >>>>Shophound, I'm not sure I'm reading your critique correctly, but are you suggesting that ducts in general are problematic? >>>> No. It is where people often choose to place ducts that create problems. * Ducts in attics = HVAC capacity loss and possible building pressure concerns due to...
  8. Shophound

    Fan Screeching Noise

    Check sheave wear while you're at it. Sheave grooves should be v-shaped, not dished. Also consider going with cogged belts unless you are already using them.
  9. Shophound

    HVAC apps for smart phones?

    HVAC Buddy for service techs is good. Allows the user to plug in parameters to obtain target superheat/subcool and target temperature deltas across a cooling coil. PsychromeTree, available for Apple iOS devices, is also very useful. It's a psychrometric calculator/converter.
  10. Shophound

    single family residence in southern calif

    Using wall stud cavities for air transfer is most often a BIG mistake. Unless you can guarantee the entire run of that cavity is airtight to anything outside of the conditioned air moving through it, you will encounter building pressurization/depressurization concerns, which often translate to...
  11. Shophound

    single family residence in southern calif

    I lived in San Diego for eight years, so I'm familiar with So. Cal winters. Not harsh, to speak directly to the point. Less than 20% of the year for heating degree days. Lots of shoulder weather. Pick your climate based on how far you live from the ocean. Further inland, the hotter it becomes...
  12. Shophound

    single family residence in southern calif

    I also don't quite get the objection toward one air distribution system for both heating and cooling modes. Truth is, do the building envelope right and the need to push air around at high volumes decreases. Comfort levels increase. Comfort is more than just correct temperature of the air. It's...
  13. Shophound

    Chilled water GPM ?

    Does the chiller unload 10% every time you add water directly to the loop, or was it only a one time observation?
  14. Shophound

    Minimum Temperature requirement for keeping the pipes and equipment freezing

    What temperature do you want to keep the abandoned areas at? Say you pick 40 degrees to give you a buffer against freezing any pipes running through the abandoned section. From there you can figure how many CFM are required at your winter outdoor design day conditions to hold that space at 40...
  15. Shophound

    Chilled Water / Hydronic Training

    2008 ASHRAE Handbook - HVAC Systems and Equipment, Chapter 3, is a good place to start concerning central plant/chller plant design.