Hi Guys,
I'm finding difficult to inteperate T 250.66
I have two parallel conduits, each having 2#500 kCMIL and 1#1/0 GND conductor. How do I size the grounding electrode?
T 250.66 says to consider equivalent area of ungrounded parallel conductors. One 500kCMIL has the area of 0.7073 in.
Thanks
Hi Guys,
I have an unbalanced delta load. Phase AB 7.7Amp Phase BC 7.7 Amp Phase CA 7 Amp.
The power is also supplied form a delta source.
I have also calculated the vector IAB = 7.08+3i, IBC = 7.08+3i and ICA = 6.44+2.73i
Also IA = - (0.644+ 0.27i)
IB = 0+0i
IC =...
Hi Guys,
I'm doing a lighting design for interior lighting.
To find the total # of luminaries I need to know the "coefficient of utilization" (C.U.)
I have effective reflectance of ceiling and walls as 50 and 10 respectively. And the room cavity ratio (RCR) is 0.54
When I look up the table...
I'm not gettting it. The length is fixed based on supply voltage and and the Circuit Breaker size. I don't have any problem with that.
I'm using self regulating cables but it really doesn't matter much what kind of cable you are using to determine the circuit breaker size. The method for...
Itsmoked,
Let me put it this way. The normal operating current(at ambient temperature) is 18.5Amps.
But if the heater is to START at -20 degree centrigrade, the heater would require more current then the normal current. I would like to know that 'starting current'. Any factors or formule for...
It does not say about sizing a breaker.
All I know is the CB should be sized based on ambient temperature (which is -20) in my case. This is based on the fact that the heater will draw more current as the temperature drops.
Hi Guys,
Can anyone provide me the formula for calculating the 'start up' current for heat tracing?
If I have normal heater operating amps 18.5 A, How would I determine the 'start up' current?
Thanks.
Table 408.56 gives information on minimum spacing between bare metal parts.
I have 600V systems and clearance between two bus bars is just 3/8 inch! (should have been 1 inch according to the code)
What could be the possible suggestion to overcome this?
Thanks for reading.
Davidbeach,
What do you refer a 'ground' conductor? Terminology is NEC is confusing. Here's how I interperate,
ungrounded = hot
grounded = neutral
grounding = ground
Thanks DanDel,
Clear about my 1st doubt.
In my second question,
First paragraph-I assumed that there is a ground fault ( a hot conductor touching a metal surface). It is just a background anyway.
Second paragraph-I am assuming that the conductor is not insulated and somebody intentionally...
Bonding is the connection of all electrically conductive materials (which are likely to be energized) to each other and to the neutral conductor in order to create a low impedance fault current path, back to the source.
My question is.
1. Since the neutral conductor also has current in it, will...
I have been working with photovoltaic sytems so the power that I was talking about was not from any dc motor or such.
I got the answer. Thanks burnt2X, davidbeach and everybody for sharing.