Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Roshan07

  1. Roshan07

    Conversion of 3PH 480V 60Hz Supply into 3PH+N 400V 50Hz Supply using Static Frequency Converter

    'Now you want to put on a static converter? Wow. Don't go there." Why not? Any reasons? please clarify. Could you explain the "No, the reason is you put 680v square waves into the equipment, with 1200v spikes on top of it!" 480V 60Hz is the system supply voltage. The output of the VFD is 400V...
  2. Roshan07

    Conversion of 3PH 480V 60Hz Supply into 3PH+N 400V 50Hz Supply using Static Frequency Converter

    The AC Panel with the VFDs feeds 1. Two Closed Control units (CCUs) -one duty and the other Standby 2. two Outdoor Split Units (FCUs & CUs)- one duty and the other Standby 3. Tow Indoor Split Units (FCUs & CUs)- one duty and the other Standby Each of the above 3 sets are fed from a single...
  3. Roshan07

    Should there be isolation betweeen base of Air terminal and the metal roof on which it is installed?

    In one project, we are installing Lightning protection System on a tall building, which comprises of both Concrete Building sections and metal roofed sections. There are Air Terminals installed on supports fixed to handrails. There are Air terminals installed on metallic columns and the metal...
  4. Roshan07

    Conversion of 3PH 480V 60Hz Supply into 3PH+N 400V 50Hz Supply using Static Frequency Converter

    In a project on an island offshore Abu Dhabi, UAE, the system voltage available is 3phase 480V 60 Hz. Due to the time constraints the HVAC equipment supplied & installed are of 3Phase+Neutral, 400 V 50 Hz. A solution to convert the 3PH 480V 60 Hz into 3PH+N 400V 50 Hz was made through a VFD...