@Masius : It is not exactly what I wanted to post here. Thank you!
At delta side I have a 33 kv switchgear and one of the outgoing feeder is connected to a Zigzag - Aux transformer.
The Zigzag-Aux transformer in my project is 50kVA. How much have you limited L-G fault by use of Zigzag Tr and NGR?
@Kiribanda : Thanks for the inputs.
We need LV supply and therefore we would like to have a mix of earning and auxiliary transformer at least 50 KVA 33/0,4 ZNyn.
From an old zigzag earthing transformer, i found ghe short circuit impedance Zk% is around 5% and zero sequence is 110/phase.
Without...
I am currently working on a 33 kV distribution system, and i must design a Zigzag earthig transformer+ NGR on the secondary side of a 132/33 kV Yd transformer. I need a sample calculation file. If you have any sample files available, I would greatly appreciate it if you could share one with me.