  1. redox

    Control wire numbering

    I am looking for a standard number (prefarable IEC, but reference to any other standard would also be helpful) regarding the numbering of panel-wires. M is for instance a motor circuit, C10 a protection CT circuit on the red phase, B a busbar CT circuit, J the DC control voltage, etc. Thank you...
  2. redox

    Single phase to ground fault calculation

    jghrist: No motor contributions. See it as a transformer feeding a bus, with the incomer to the bus open. Thus, just the transformer energized. Now I understand that that the fault-current would be 3Io, but why are the software-calculated current so much higher than the hand-calculated...
  3. redox

    Single phase to ground fault calculation

    Thanks for both of you. The intention of my hand-calculations is to ensure the software calculations are correct. Kind of a double-check or a check-up. Literature indicate: Ia1 = Ia2 = Iao = Ea / (Z1 +Z2+ Zo) Do I have to add the three together? Ia1 + Ia2 + Iao = Ifault And what will the...
  4. redox

    Single phase to ground fault calculation

    I am doing a three phase and a single phase to ground fault calculation on the secondary side of a transformer. But the answers I obtain from my software-program and the answers from my hand-calculations (invinite bus) are not the same - somewhere I am doing something wrong. Trsf data: Rating...
  5. redox

    Use of Y-Y Transformer in replace of D-Y

    If I may ask: Will there be any differences if a Wye-wye transformer is used, but the primary neutral is not grounded? Thanx
  6. redox

    Time for start-up between two motors

    Thanks all! The motors are not on the same pulleys. (2 pulleys on one belt) There are fluid-couplings between the motors and the gearboxes. The problem is that one motor can't take a fully loaded belt away on its own. (Without any material on the belt there is no problem) With a long delay...
  7. redox

    Time for start-up between two motors

    We have two motors on a conveyor belt (Each 50kW) How do you determine the time-delay between the start-up time of the two motors? (DOL-starters) I don't want to start both imediatelly (due to the high start-up current), but I also don't want the time-delay between the start-up of motor1 and...
  8. redox

    Motor data

    Thanks for the replies. jb: The only nameplate data avaliable is the data in my first post. There is 4 different size motors (Slipring motors, same manufacturer) The only data again: Motor 1 Power: 500kW rpm: 1483rpm Stator V: 3300V Stator I: 115A Rotor V: 855V Rotor I...
  9. redox

    Motor data

    I want some data on some old WRIM-motors we use in our plant, to check their settings. The manufacturer doesn't exist anymore, so I don't know where to obtain the data. Can I assume any values or is there any average value I can use for: 1. Safe hot stall time? 2. Permissible start attemps /...
  10. redox

    CT kneepoint determination (IEC ratings)

    Hi all Is there any way how you can determine the kneepoint of a protection CT with the nameplate values?(IEC ratings) To determine the kneepoint with a voltage source and a ammeter is no problem - I want to know if it is possible to find it mathematically. Thanks
  11. redox

    I have a question re relay coordina

    Thanks again for all the replies Maybe my original question is a bit confusing - so let me try again 10P10 1000/1 CT's Earth fault current 8000A E/F relay setting on 10% (pick-up 100A) but relay is effective up to x20 plugsetting (effective up to 2000A - earth fault current is 8000A (x80 of...
  12. redox

    I have a question re relay coordina

    dpc: Thanks for the reply! I have no problem with the time-interval between the relays. My problem is on which current to add the 0,4sec. In the example I've used when I started this thread (10% setting), the relay will be effective up to 2000A, but on higher currents it will not - I think...
  13. redox

    I have a question re relay coordina

    I have a question re relay coordination on electromechanical IDMTL earthfault relays. Take a system with 10P10 1000/1 CT's. Relay is 2xOC and 1xEF. Take a earth fault setting of 10%, meaning that the relay will pick-up at 100A. Most relays claim to be effective up to x20 plugsetting, in this...
  14. redox

    Coordination between hi-set unit and IDMT-relay

    What is the time interval between a high-set (instantaneous) unit and IDMT-relay? I know time between relay-relay is 0.3 - 0.4 seconds, is it the same between high-set and relay or not? Thanks
  15. redox

    Resistors in rotor-circuit

    Thanks for all the replies! Due to unforseen circuimstances,I haven't been able to reply to your responces. Marke: I'll give you a red star for your comments. jraef: You are right, this is a overland conveyor system (iron ore) jbartos: I am not sure what you asked, but like I said, there is...