  1. racobb

    Bypass an off neutral regulator

    OOPS! Realized my mistake after the post and re-reading your OP. Alan
  2. racobb

    Bypass an off neutral regulator

    Is the switch a single pull bypass/disconnect? Alan
  3. racobb

    Bypass an off neutral regulator

    If I am understanding correctly, there appears to have need no reason to close the bypass at all. Line and load side switches could have been closed and then the breaker if at a substation. Sounds like it may be a single phase line and regulator down line from the station except that there...
  4. racobb

    Bypass an off neutral regulator

    Well, they can easily be moved if the line side blades/switches are closed from a powered bus. Also to add one step to crshears well detailed routine, I also turn the control power off after running it to neutral and verifying the position indicator and neutral light prior to bypassing. One...
  5. racobb

    Transfomer tap changer vs voltage regulator

    Another advantage to individual circuit regulators is the ability to keep a spare unit or units on hand for quick replacement and.....only one circuit affected at a time. I think the standards require a minimum fault rating of 25 times the base load current raring of the regulator. Don't have...
  6. racobb

    NiCd and Lead acid battery Charger

    Have you passed this by the battery manufacturers yet? They could probably provide some valuable suggestions. Alan
  7. racobb

    Getting power from solar panels under transmission lines

    Disadvantages? Unless you are the utility that owns the line, you will have to deal with the right of way restrictions in place, an may still even if you are the utility. Most utilities that I am aware of here in the states do not allow placement of anything permanent, other than possibly a...
  8. racobb

    Transformer Impedance and Full Load kVA

    You have gotten several reputable references right here. You just need to heed the advice as you are not grasping the basics with this. These guys are correct....and to quote DRWeig.....'nuff said. Otherwise, you really need to hit the books! Alan
  9. racobb

    Transformer Differential Trips

    This is in a substation that feeds outgoing utility distribution feeders with all combinations of loads. Zero sequence removal is done with the settings. I was reminded today that for 2 to 3 months the transformer had between 15 and 20+ MVA on it while another station was down for maintenance...
  10. racobb

    Transformer Differential Trips

    No I am not completely sure. But for now the transformer mfg. stills owns it since it is still under extended warranty. The mfg. has blessed its return to service, but I want to make sure I have data the next time.....if and when! BTW it is ONAF. Thanks!!! Alan
  11. racobb

    Transformer Differential Trips

    norcalnewb, We did use it prior to commissioning and have checked since. Have not input measured values though. Plan for now is to replace the relay and do another complete wiring check and testing. Thanks Alan
  12. racobb

    Transformer Differential Trips

    dpc....agree that there are many wrongs and only one right. To clarify, the system faults I referred to are on the distribution system fed by the transformer, so they are through faults. pwrtran....cabinet heaters are working and all is clean and dry. Most recent trip was on a beautiful dry...
  13. racobb

    Transformer Differential Trips

    On an additional note, the single phase excitation tests went well today with no problems. Alan
  14. racobb

    Transformer Differential Trips

    Thanks to all so far. I made myself a promise in about 2009 never to install a critical relay unless it had memory for an event/fault history with vector data. This unit has been loaded to approx. 5000 kW during its life so far. We have had numerous system disturbances with breaker trips to...
  15. racobb

    Transformer Differential Trips

    Looking forward to input! In summer 2008 we commissioned a 20/27/33 MVA, 115-25 kV, Delta-Wye substation transformer. Subsequently we have had 3 differential trip events on the unit and have yet to determine the cause. Except for thes ethree events the transformer has otherwise been in...