Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by psugreen

  1. psugreen

    VAV Duct Design Question

    Looking for sizing parameters for the higher pressure ductwork upstream of vav between the vav and the air handling unit. Do you look at friction rate and velocity? Or just one of these?
  2. psugreen

    VAV Duct Design Question

    .08-.1" wc / 100 ft on the low pressure side downstream of the vav box correct? What paramaters do you use upstream of the vav box?
  3. psugreen

    VAV Duct Design Question

    When designing duct upstream of vav boxes do you size for both upper limits of velocity and friction per 100' of duct? What limits do you use I.E. Velocity limit of 2500 fpm and friction of .3" per 100'. Or do some size based on just velocity or just friction? (If you sized purely based on...
  4. psugreen

    Steam Line Sizing

    When sizing a steam line to an AHU coil, should the branch lines going to the ahu coil be the same size as the coil connection size or is it ok to use a smaller size? When using the size charts it looks like a smaller size would be acceptable but I think I remember reading somewhere that...
  5. psugreen

    VAV Duct Design

    Application is a typical office building. There must be a range that is used for static or velocity?
  6. psugreen

    VAV Duct Design

    What static and velocity do you use when designing vav ductwork upstream of the vav boxes?
  7. psugreen

    Pump Selection Questions

    2 questions in relation to pump selection: 1. For inline pumps should suction and discharge connections be line size, or is it ok for the pump to have a smaller connection than the pipes it connects too? 2. What is the best speed (rpm) to select pumps at?
  8. psugreen

    Multiple Inline Exhaust Fans Sharing Discharge Duct

    In parallel. They would share the same discharge duct only.
  9. psugreen

    Multiple Inline Exhaust Fans Sharing Discharge Duct

    This is general exhaust controlled by t-stats (large storage / mechanical / electrical rooms that call for exhaust/makeup to keep temp 10 degrees below ambient). I would put backdraft dampers at the discharge of each fan. They would not necessarily be running in unison. Some could be off...
  10. psugreen

    Multiple Inline Exhaust Fans Sharing Discharge Duct

    What are your thoughts on using one discharge duct for several inline exhaust fans? Is this an acceptable practice? Anybody run into problems doing this?
  11. psugreen

    Pressure Drop (Pump Selection)

    Does anybody have a software program or spreadsheet that they use for calculating pressure loss (ft of head) for hydronic systems to assist in pump selection.
  12. psugreen

    Psychometric Equation Question

    Thanks all for your help. The link for the @air program that UtilityLouie referred to is http://www.techwareeng.com/prodAA.htm. They have a 30 day trial version that I'm going to try out. Imok2, the equation I'm looking for is enthalpy when you have known dry bulb and wet bulb temps which is...
  13. psugreen

    Psychometric Equation Question

    Is there an equation that could be plugged into an excel spreadsheet to calculate enthalpy at a known dry bulb and wet bulb temperature? Or is there a equation for total energy with known entering and leaving dry bulb/wet bulb air temperatures?
  14. psugreen

    Ventilation Rates For Doctor Offices

    I'm working on the hvac design for a new doctor's office. Does anybody know where to find minimum ventilation rates for exam rooms, treatment rooms, x-ray rooms, labs, etc? I don't think ASHRAE 62.1 covers this area.