  1. polyphase

    Distributed Generator Paralleling Device

    Well said, Davidbeach and dpc. That is a complete and concise answer.
  2. polyphase

    Requesting References or Descriptions of Existing Power Systems

    I am a member of the Working Group developing IEEE P1547.2 Draft Application Guide for IEEE 1547 Standard for Interconnecting Distributed Resources with Electric Power Systems. We are including a general description of power systems. This information should be helpful since the siting and...
  3. polyphase

    Induction motor power factor during run-up

    I hope that I can add a little to this discussion without causing more confusion. The starting PF does matter. dV = I(R cos phi + X sin phi), where: I = LRA of the Motor R = The System Resistance (Cable + Source) X = The System Reactance (Cable + Source) cos phi = Starting PF of the Motor If...
  4. polyphase

    2nd Harmonics caused by a three pulse rectifier

    What remediation techniques are available to manage the 2nd harmonics being injected into the AC supply by a three pulse rectifier for a DC motor? Reportedly, the total harmonics on this service exceeds the IEEE 519 limits. The harmonics are predominantly 2nd, 3rd and 5th. If the load...
  5. polyphase

    Mathematical Vs Power Engineering convention (Power Factor)

    weh3, I would appreciate seeing more regarding your spreedsheet graphing.
  6. polyphase

    Induction Vs Synchronous motors for paper mill

    What are the decision making advantages / disadvantages for choosing induction or synchronous motors for industrial applications such as paper mill refiners? The sizes are 1,000 to 3,000 HP, and the voltage is 2.4-kV. The mill is served by a 33 MVA 115/12.47-kV transformer, and the expansion...
  7. polyphase

    Fault Indicators for overhead lines

    Here is another guess at a possible reason. The phrase "safely installed some metres below conductors" implies a difference in the work practices necessary to install the two types. One requiring hot line work and the other being less hazardeous. Also there is the quanity issue of...
  8. polyphase

    How do I Size a Grounding Bank for a Delta Source?

    The situation I have is a 24.94-kV four wire grounded system normally serving load through a 24.94/12.47-kV delta/wye stepdown. Both the 12.47-kV and the 24.94-kV are four wire grounded wye systems. There is a desire to reverse the flow and serve several customers on the 24.94-kV side from a...
  9. polyphase

    Power Distribution Unit problem

    The voltage drop through transformers is a function of the load power factor and the X/R ratio of the transformer. A transformer may have a voltage drop of less than 1% when loaded to 100% of its MVA or KVA rating with a unity(100%) power factor. The same transformer may have voltage drops of...