Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by pittengineer

  1. pittengineer

    Industrial plant incoming voltage regulation and voltage drop

    Spoke with utility and they tell me that the are regulating secondary voltage (tap changer) to 120V on the secondary of the 2400V to 120V PT's with the PT connected L-N on 4.16kV secondary. They said that there is a 2V bandwitdh on tap changer. This means that they are regulating secondary to...
  2. pittengineer

    Industrial plant incoming voltage regulation and voltage drop

    We've also noticed that this drop is occuring plant wide and even measuring minimums of 109V in office receptacles during certain times. Would this be an indication that we should raise or incoming voltage to some amount? I'm going to look into the two measurment errors mentioned. Might be PT...
  3. pittengineer

    Industrial plant incoming voltage regulation and voltage drop

    We are having an issue where an 120V branch circuit is dropping to 112V during the starting of a motor and causing problems with electronics. This voltage drop is causing several problems and we are searching for answers as to what we are seeing and where to make corrections. Our system has a...
  4. pittengineer

    Earth Resistance Testing in a large industrial facility

    dpmac I have seen the same MSHA standards that you are referring to, and although they do state that these systems need to be tested anually, they are very vauge in what they are looking for. Its hard to decipher weather or not they are looking for a test to be performed at every transformer...
  5. pittengineer

    Earth Resistance Testing in a large industrial facility

    Zogzog I am indeed having a NETA certified testing company perform this testing. I am confident that they indeed know how to perform a 3-point fall of potential test, however there seems to be some confusion even with them as to may many points we need to test, and at what locatins since grid...
  6. pittengineer

    Earth Resistance Testing in a large industrial facility

    I have been requested to perfrom an earth resistance test here at our industrial facility. This tested is mandated by MSHA requirements that govern our site. Our distribution voltage is 4.16kV and our utilization voltage is 480V. I have been researching this test and plan on performeing a...
  7. pittengineer

    VFD design for centrifugal pumps

    I jsut recieved a quote for the same drive in a 40hp and it still came in at $15,960.00 which is high. I'm probably going to do just as DickDV mentioned and get rid of the additional HMI if I pursue this drive. Do you guys think that after removing the HMI I should be paying under 5k for this...
  8. pittengineer

    VFD design for centrifugal pumps

    I just recieved a quote for one of these Powerflex 70 50Hp drives at about $17,300.00. This included the drive mounted in a NEMA 4 enclosure with an HMI mounted on the front of the enclosure. It also included a 3% line reactor installed in the cabinet on the line side of the drive as well as...
  9. pittengineer

    VFD design for centrifugal pumps

    Thanks for all the responses guys. After reading all of the respones it sounds like trying to use one drive to control both motor will be too complex to integrate into the existing control system and may only lead to problems with maintnance and operation. I am still awaiting pricing on...
  10. pittengineer

    VFD design for centrifugal pumps

    Waross Good point about adding a second breaker for redundancy on the bypass contactor. I was thinking as well that if one of the motors failed and tripped the breaker it would leave us dead in the water. I am awaiting on pricing for just the standard drive to see how much each drive costs to...
  11. pittengineer

    VFD design for centrifugal pumps

    Just thought of an idea to run the motors DOL if there is a problem with the drive. Where the drive is located, or in the drive enclosure I will add a 3rd contactor which esentially bypasses the drive if there is a problem with the drive. The contactor will be on the load side of the thermal...
  12. pittengineer

    VFD design for centrifugal pumps

    I apoligize but I realize now I forgot to mention a key piece to all of this in that these two motors are already connected to individual starters running across the line. I am wanting to retrofit this setup to incorporate a vfd. Davidbeach brings up a good point in that with only 1 drive we...
  13. pittengineer

    VFD design for centrifugal pumps

    I am putting together a design for a VFD controlling two 40hp motors on centrifugal water pumps which are pumping water from a tank. Only 1 motor ever runs at a time and the other motor is strictly sitting on standby as a backup. The idea is to control the speed of the motor and thus the flow...
  14. pittengineer

    Should I replace damaged stator RTD in 350hp motor

    The motor that I am referencing is a 350hp 4.16kV induction motor started with a DOL starting method. The motor came equipped with 6 stator rtds which are connected to a motor protection relay for monitoring. It was discovered recently that one of the rtd's was damaged (failed open) and was...
  15. pittengineer

    cable overheating

    Getting back to Turbogen's comment above about "Induced Eddy Currents". Aren't these induced currents and eddy currents that you spoke of magnetic flux currents as opposed to actual electrical currents. Wouldn't it be the same as if you wrapped a coil of wire around a core, with the current in...

Part and Inventory Search