Vanda106
The short circuit impedance has a definite affect on the peak inrush current. High inrush currents occur when the core saturates during the energization. Once the core saturates the current is the voltage divided by the impedance ohms of the transformer.The point at which the core...
You CANNOT use the 64 amp rating when the wire is used in an Air Core reactor. Air core reactors can have high eddy currents. Also the wires are blanketed with insulation. Usually the current density in air core reactors is 2000 amps per square inch or less. 64 amps looks very high to me
A shunt reactor is a reactor connected line to ground. A series reactor is connected in series. and a capacitor bank is a number of capacitors in a series parallel arrangement usually connected line to ground.
The Z= 6% Simply means the maximum short circuit current is
100/6 = 16.67 times normal = 300*16.67 = 5000 amps
Also it means the reactor is rated .48 ohms
2400 volts/.48 = 5000 amps
Also if the 1.7% is mostly reactance and the short circuit occurs at a voltage zero, the the peak asymetrical current could be 18.4 X 2 X 1.41 = 51.9KA
Precipitation transformers are typically less than 100 KVA and are Rectifier transformers used to remove smoke particles.
Transformers used to test other transformers sometimes require a shield also.
Ahandle -- This is sometimes called an "Electrostatic shield". and is usually required when the secondary winding is subjected to arcing. For instance most precipitation transformers require this shield. It is usually a 10 mill copper sheet placed over the secondary winding and then grounded. (...
I disagree with Magoo2. Air core reactors are more prone to vibration problems than Iron core. As the reactor traverses from zero to its peak current the reactor forces are trying to expand the diameter and shrink the height. Since a shunt reactor sees only rated current these forces are not...
KMH1
What are the dimensions of the reactor? You mentioned a single phase reactor, but I see (3) reactors in the picture. It looks like a (2) layer design reactor. I assume the the layers are in parallel not series. It could be that the volts per turn are too high. Also shunt reactors are...
I agree with rcwilson except his multiplier of "10 - 12 times". This amount of inrush only occurs if the core saturates. Since the applied voltage is well below rated, the core will not saturate. If the transformer is energized @ a voltage zero, then the multiplier will be a factor of 2 not "10...
Filter reactors are basically shunt reactors. They are connected in series with a capacitor to create a low impedance path to ground for certain frequencies. A current limiting reactor is connected in series and therefore cannot shunt any harmonics.