Dear All
Please see attached picture. No data for hp or amps only volts, frequency and LRA any idea of the power rating?
Thanks
Petronila https://files.engineering.com/getfile.aspx?folder=0c8c55a3-c8a2-4f90-97d2-52a1d5af9f9c&file=York.jpg
Hello Drivesrock,
I believe you can try contacting a distibutor. See contact details below:
info@alangstore.com or WhatsApp: +918264322525
Best Regards
Petronila
Just note if the motor is redesigned to 575 V, the original nameplate should be replaced: 1 hp, 575 V, 1.55 A. Also, if the core dimensions allows, the rewinding give you the opportunity to increase the power output. Even though this is a simple redesign, for avoiding early damage of the new...
NomadicOwl,
What Gr8blue is expaining is correct. However, regarding the space heaters connection just note the 120 V is a parallel connection (4 resistance connected in parallel)and the equivalent resistance is R/4; for 240 V connection the equivalent resistance is R (resistances connected in...
Waross
The problem with the centrifugal switch is real and it is a factor. You can not grant the Centrifugal Switch will works proper for the new speed. Adding a boost transformer is more expensive beceause you will need to size the transformer at leat 3 times the power of the motor and if this...
nsalhieh,
There are some important factor to consider due to incresing the RPM will increase the demanded power from pumps applications up to 1.7 tiems due to affinity laws thus even if you can redesign the winding from 50 Hz to 60 Hz you should trim the pump impeller. However, some of this...
Dear All,
I have seen some OEM use flexible jumpers for connecting the damper winding of the synchronous motors/generators (see attached pictures). I would like to know your inputs of what should be the justification for such design.
Thanks in advance
Petronila...
Zlatkodo,
"How can the motor be more powerful when the number of turns per phase is increased?: It is because the Airgap density is increasing due to the interaction of the CF reduction and number of turns, thus the torque increases; at the same RPM the motor will be stronger. You will note...
Hi Pete,
Please see the attached Table.
Mutu "For 12 turns (N in the table) single layer concentric with those pitches, equivalent double layer will have 7 turns with 1-19 coil span": That´s the reason why you should not use the 1-19 pitch because you will drop off the wire area and will be...
Dear all,
Converting to lap this concentric winding will have very few reasonable options available, rougly speaking about the AC motor redesign the key is to keep the magnetic densities in the airgap, back iron, and tooth in +/- 2 %. Normally the main guidance is the airgap density that varies...
Hi Wba1,
Motor are connected in a Dahlander variable torque connection. Usually, for this connection, the 2 speed power output ratio is 1/4 that is, High speed power rating is 4 times the lower speed power rating. See attached file.
Best Regards...
Dear All,
These conection is also used for running motors delta rated @ 460 V at 575 V with a 15 % torque reduction. See the technical article: A closer look at winding conversions by reconnection.
Regards
Petronila
Hi Zlatkodo,
What you are describing is not a starting method intended for reducing the inrush current this starting method is used for increasing the torque during the start, considering the rated current is Delta the motor will be starting as a "2Y connection" and the inrush current will be...
Dear All,
This one should be a small motor so harmonics can be handled. It is possible to redesign to lap winding but with two different coils per slot you will need to add a separator and maybe there is not enough room in the slot for it.
Even though the preferred pitch should be 1-4 the...