Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by pauliwood

  1. pauliwood

    LV voltage Fuse co-ordination

    Dpc, it's more of a competitive issue regarding min melt and total clearing times. They publish avgerage melt curves as you said, and to get your min melt and total clearing, I believe it is +/- 10%. Has been awhile, you could confirm that Brickeletric by calling either of the fuse companies Dpc...
  2. pauliwood

    Cable Damage curves vs coordination

    Your breakers Time Current Curves (TCC) when overlayed on your cable damages curves, should appear to the left of your cable damage curves. Below 0.01s is the short circuit time frame, usually not shown on breakers as they are typically slower to open under fault conditions. Not as familiar...
  3. pauliwood

    Power XFMR 100MVA xfmr fault current

    Dpc, your calculation is correct, and that is the maximum amount of fault current the trandformer can produce. This fault current would be limited by the source feeding the primary side of the transformer. Downstream of the Secondary side, the fault current would be reduced due to the...