Driftlimiter, that was my concern, and it raised the alarm that those shear forces are not being transferred to the anchor for checking in concrete. It turns out I need LRFD combinations and design for the LRFD base plate and anchor elements for the program to check those design checks. I had...
I apologize, it does include the lateral loads (Vu3) in the huge order in the connection design. However in the design verification at concrete base it only checks the (axial bearing), what about the shear breakout in concrete 51 kips in LC41. I could be wrong this is my 1st time with braced...
Hi,
I use STAAD pro and RAM connections interchangeably. When I design the base plate with a gusset connection in RAM at the bracing locations. RAM imports the loads from the column axial, V2, & V3 shear forces, and the bracing axial force. The connection is fine, however, when I go and see...
Thank you JAE, for the connection between the metal deck to the supporting beam is it ok to consider the Headed studs welded as the attachment and get rid of the powder actuated fasteners ? This makes the beam and deck to act compositely as well
Hi,
To consider as a composite deck slab (1.5"x18GA. metal deck with Normal weight concrete topping, total slab depth = 4.5") and use the composite deck slab load table to determine the allowable superimposed loads.
The connection of the metal deck to the supporting beam underneath, should...
Thats where I was going to, when the beam-column connection is designed for shear as well as axial loads, it should be fine.
However, I was playing with Ram connections and in the program for this particular case, where there are beam on both sides of the column the program doesn't consider...
But then, the beams are connected to the column, and then they maintain the continuity for the collector/ chord system right? via shear tabs or however, the beam column connection is
Hi,
In the roof diaphragm, as shown in the below detail, what is the need for this tie 3/8" plate? if there is a beam on both sides of the grid along this diaphragm line (J) and this line has a vertical brace frame positioned, could this 3/8" tie plate detail eliminated?
With vibration, checked for the floor framing system (metal deck with concrete), and the floor beam configuration was ok, but didn't link that to the OWSJ connection with hangers. One end of walkway is connected to regular beam/ column and other end to the hangers and to roof joist
Hi,
There is an 80-foot span open web steel joist, and apart from the roof loading, it also picks up the floor walking track hung through the hangers. In this case how to go about the deflection limit, the Live load limit L/360 allows 2.67" and total L/240 allows 4". These look large value...