Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by paliha

  1. paliha

    Earth switch in incomer

    Incoming supply is from city power. So electrical interlock is also not possible. Only option may be to used DS with earth position. Appreciate your response.
  2. paliha

    Earth switch in incomer

    I am sorry the attachment was not included. Please have a look now.https://files.engineering.com/getfile.aspx?folder=e0c9aa6f-c095-4001-adf0-eb603067ac15&file=Earth_switch.pdf
  3. paliha

    Earth switch in incomer

    I have seen earth switch (ES) on the 33kV incomer cubicle of the switchgear. It may be a requirement for the supply authority to ensure no power will be fed back during maintenance etc. My question is how to provide interlock to ensure the ES will not be operated while incoming supply is...
  4. paliha

    Data communication using GSM network

    My object is data transfer between three pump stations and central SCADA station using GSM network. I came across SINAUT MICRO SC - software together with GSM Modem MD-720-3 which i feel is very close to my expectations. What i am not sure is, whether static IP will be required for the...
  5. paliha

    Communication betweem different PLC

    Hi djs, The make of the other PLC is not decided yet It has to be through competitive bidding and therefore it may be any make. Actually that is the main issue.
  6. paliha

    Communication betweem different PLC

    Hi djs, The SCADA will be connected to other PLC as well, within the water treatment plant and secondary pump stations. I will upload a system diagram which gives more information. Please have a look...
  7. paliha

    Communication betweem different PLC

    PNachtwey, Thank you for the information. It looks like an emergency exit. Thanks.
  8. paliha

    Communication betweem different PLC

    Hi djs, Thank you for the reply. The SCADA side equipment are not yet decided, and will be decided after tendering. The target is to finish with the first guy and have everything ready for the second guy to move forward with his work without interaction with the first guy. (but seems...
  9. paliha

    Communication betweem different PLC

    Hi IRstuff, Thank you for the reply. I take ICD as a good idea to start with. Regarding the protocol the first guy has agreed to go with any common one, but i will not know the preference of the second guy. However i do not think it will be a serious issue if common one is selected. I am...
  10. paliha

    Communication betweem different PLC

    Hi, I am involved with a project where information from an existing PLC is to be taken for the purpose of monitoring by a SCADA system. Basic information are indicated below, Existing PLC - Siemens SIMATIC Application - Filter control of a water treatment plant Initially we planed for using...
  11. paliha

    Electricity Bill - Peak Power

    The power factor we measureement with standard PF meter makes use of displacement of voltage and current phases, and when we measure PF with such meter, we observe good power factor for VFD drive. Or even leading PF due to the DC bus capacitors. However due to the harmonic currents generated by...
  12. paliha

    High capacity raw water pumps - Submersible or vertical shaft driven pumps

    Hi all, Thank you for all who have given comments. It is good advise from JJPellin not to go for "smallest, fastest, largest or longest of any particular technology" It is applicable in this case. River sand is a problem for vertical turbine pumps, but main option we consider is vertical shaft...
  13. paliha

    High capacity raw water pumps - Submersible or vertical shaft driven pumps

    Hi all, Decision between submersible and vertical turbine pumps for raw water pumps has been discussed under thread 407-233951. But my problem is more towards high capacity end in the region of 1250 L/S at 40M. (750kW) Decision is almost made in favor of vertical shaft driven pumps, mainly...
  14. paliha

    VFD Driven motor efficiency

    waross (Electrical) 21 Jun 12 5:54 Try checking the efficiency without the VFD in the circuit. There is no bypass contactor- The contractor is not ready to do a temporary wiring. So it is difficult. . DRWeig (Electrical) 21 Jun 12 8:50 I'll amplify waross' second statement: Pump...
  15. paliha

    VFD Driven motor efficiency

    Hi Friends, I have a question regarding the overall efficiency of VFD Driven motors. Normally the VFD efficiency is around 96% and motor efficiency around 94% (around 30kW range). When we made a measurement for a motor used in pumping system, the overall efficiency fell much below the...