Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by NEWFIEBOY

  1. NEWFIEBOY

    ABB SYNPOL D power management, alternator protection.

    Hi. I have a problem with one of these ABB alternator protection units. I am looking for a web site where I may be able to find technical information or a troubleshooting guide. I have googled ABB SYNPOL D but I am not finding any down loadable technical information. I am wondering if any of...
  2. NEWFIEBOY

    Grounding in ships

    The electrical system you are describing sounds like what we refer to as a hull return system. The generators would be connected in a Y or star pattern and the neutral point would be connected to the ships hull. The phase to phase voltage would be as you state 415V. The phase to hull voltage...
  3. NEWFIEBOY

    Proportional Output Thermostat

    There is a thermostat which is used on dairy farms to control the barn ventilation fans. These controllers are used to control the motor speed of a single phase exhaust fan motors based on the ambient temperature verses the desired temperature. I can not give you the manufacturers URL right now...
  4. NEWFIEBOY

    SSR for motor control

    Hello Mechd07 Why not contact the manufacturer and ask them what would happen if you were to supply an overfrequency to their SSR.
  5. NEWFIEBOY

    Power Wiring for branch circuts

    Bigdog As and example, if you were to look inside a residential clothes dryer. The electrical code requires you to install a 30 amp circuit breaker in your electrical panel and to use a 3 conductor # 10 awg cable to bring the power to the dryer. Once the power is delivered inside the dryer it...
  6. NEWFIEBOY

    Power Wiring for branch circuts

    hi bigdog what exactly is your electrical engineer saying that you do not agree with?
  7. NEWFIEBOY

    Can I run a motor into the SF on an extended basis?

    Is there a down side to going with the larger motor and vsd such as cost, availability or installation concerns? If not why take a chance on the smaller motor?
  8. NEWFIEBOY

    Elementary motor wiring

    I agree with waross, some consideration should be given to the ventilation requirements of the motor. If air flow is restricted the motor will most likly over heat. Also, depending where you live or where this unit will be used, there may be some electrical code requirements which need to be...
  9. NEWFIEBOY

    Elementary motor wiring

    Hello insideman what is your voltage supply? 230, 460 etc.
  10. NEWFIEBOY

    Wound rotor motor

    Hello sed2developer There is a ground detection system attached to each buss bar at the main switchboard. The ship's electrical system is 3 phase delta with no grounded conductors. The ground detection is accomplished by putting 3 pilot lights in series and a normally closed push button between...
  11. NEWFIEBOY

    Wound rotor motor

    Thanks for all the replies. Jraef do you have an opinion on which manufacturers drive would be more suitable for this application and why?
  12. NEWFIEBOY

    Wound rotor motor

    Hi guys The motor starter does have contactors. The Original timers were changed to Omron timers, the romote control switches are now Allen Bradley. These modifications, as well as others have been carried out on as needed basis. One of the problems which we have now is that the contactors will...
  13. NEWFIEBOY

    Wound rotor motor

    Hi Guys I have a 1960s 15 hp 230 volt 3 ph wound rotor motor. It is presently connected to a motor starter and resistor bank. The motor is reversable and can be operated at either of three speeds selected by remote control switches. This motor is the power unit which operates a capstan on the...
  14. NEWFIEBOY

    motor lead to line connections

    I am not aware of any actual code requirement where you have to use a specific type of cable splice for motor lead to supply line connections. I do not like to use wire nuts, but if I have to because of motor location or space restrictions etc. I always tape them. I prefer to use split bolt and...
  15. NEWFIEBOY

    More GFCI Breaker Mysteries

    mercurous I agree with dcp, it smoked and DaveKillens power bars and GFIC circuit breakers do not seem to work well together. As the guys pointed out the surge protector internal circuitry tricks the GFIC circuit breaker into thinking that a ground fault has occured and it trips off. You may not...