  1. mvujica

    Fuel tank problem

    Thanks all for great advices, I contacted the manufacturer and the problem is that factory connecting kit for tanks is rated for flow of only 20 l/h, our contractor had installed heating oil tanks and never checked the ratings. Obviously this configuration can not withstand flow of 200 plus l/h...
  2. mvujica

    Fuel tank problem

    Where ever, our tanks are located just below the gen-set outdoors so there is no need for day tank.
  3. mvujica

    Fuel tank problem

    All our standby generators have fuel return line, the one we are talking is caterpillar C32 1000kVA generator. I belive all have constant speed fuel pump so there must be return. As I said in first post I belive that about 200l/h of fuel is returned to the tanks at our current load of 120kW as...
  4. mvujica

    Fuel tank problem

    Have you seen the Schütz drawings? It is factory kit for connecting multiple tanks, but there is no return line from generator to tanks as we have. What do you thik about my idea to put separate piping and connecting the tanks so they will level naturaly also than I can remove three inlet and...
  5. mvujica

    Fuel tank problem

    I see your point BigInch, but after a while level in tank D will be lower than of A-B-C and the pump will draw more fuel from B and so on until there is again equality? Bottom piping is not an option since these are plastic tanks (originally used for heating oil, tanks and fuel supply...
  6. mvujica

    Fuel tank problem

    Our stand-by generator fuel tanks are four 2000 l plastic tanks in arrangement shown in attachment. Gen-set full load fuel consumption is around 230 l/h but average consumption is around 25-30 l/h so 200 l/h gets returned into tanks. After long power outage of 24h we noticed that tank levels are...