It is a mistake by the concrete contractor. He constructed the pedestal+anchor bolts with 100 mm offset by referring to old drawings. The steel contractor brought the
steel columns with revised drawings.
Dear All
Are there any specifications for the distance between splice. The contractor erected the column 100 mm outside with a stub.
He also brought the beam with its original length. Now asking for a splice of 100 mm length. Beam is HSS 500x400x tk. Usually, we will allow the splice Depth or...
Thanks Mr.Kootk
1.The section is supporting beam. Refer the sketch attached
2.The weld used is 7 mm Partial Penetration Butt weld continuously
Design of weld between web and Flange RHS 300x120x16x12
3).This is beam supporting secondary beams in diagonal pattern of concave pattern. The member...
Dear All
Thanks. I have few more questions on this
1) it is a built up box of RHS 300x120x16x12
2) Do we need to consider Axial force in the member . If not why. Any references for the same
3) If there is torsion how to consider as a part of built up weld
Regards
M.S.Boobathi
Dear All
I request to share valuable experience about "How to provide Connection design forces on Drawing ". This takes long time
OR is it acceptable practice the structural model
Regards
M.S.Boobathi
Thanks for All. It is roof skylight member already surrounded by Permanent building -No possibility for expansion
The vertical shear max is only 400 mm i can mange with 5 mm(Wall thickness 12mm) Partial penetration Butt weld . Where as capacity demands almost equal to FPBW...
Dear All
I am designing the weld for Built up box RHS 300x120x16x12 ( subjected to Axial force +small flexure)
The shear capacity = 2*0.6*0.9*fy*t*D = 2*0.6*0.9*355*12*300 = 1380 kN
Equivalent horizontal shear =Vmax*1000 *AF/I = 1380*1000N*[120X16]*150/116009344 = 3426 kN
Required fillet weld...
Dear All
There are procedures to calculate the shear studs in plate reinforced coupling beams
I couldn't see such requirements in Steel reinforced coupling beam. Are they not required.
Can i get reference (AISC /ACI) for designing steel reinforced coupling beams
Regards
M.S.Boobathi
Dear All
I am checking a HSS punch plate welded connection for the revised forces . i need more weld is acceptable to provide
18 mm weld with punch plate where as the wall thickness is only 16 mm...
Dear All
We are designing a different building skylight !! with inverted curve in both direction as attached .
how to calculate the wind speed ?
Regards
M.S.Boobathi https://files.engineering.com/getfile.aspx?folder=a24dd4c0-df35-46ce-b3f0-0d88d57182b1&file=WIND_LOAD_QUERY.png
The Reply from AISC : Thanks to AISC
Hello,
I can only find one design example that is based on Section D5 of the AISC Specification, example D7: https://www.aisc.org/publications/steel-construction-manual-resources/#37583. Engineering judgement must be exercised when determining the...